As long as it's 90C wire, then yes, I believe you're correct.

I get that the wire ampacity is 14A and your circuit current is 13.8A.
 

pv_n00b

Senior Member
Location
CA, USA
Just so folks know where this is coming from. The ampacity adjustments in Table 310.15(B)(3)(a) Adjustment Factors for More Than Three Current-Carrying Conductors applies to conductors in conduit or conductors that are bundled for more than 24". If you derate your PV DC conductors to 35% of the rated ampacity you can put as many as you want in a bundle. Ref; 310.15(B)(3)(a). A #10 90°C conductor is rated for 40A and 14A at 35%.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Just so folks know where this is coming from. The ampacity adjustments in Table 310.15(B)(3)(a) Adjustment Factors for More Than Three Current-Carrying Conductors applies to conductors in conduit or conductors that are bundled for more than 24". If you derate your PV DC conductors to 35% of the rated ampacity you can put as many as you want in a bundle. Ref; 310.15(B)(3)(a). A #10 90°C conductor is rated for 40A and 14A at 35%.
But don't forget your temperature derate.
 