How about NO
cowboyjwc said:I'm sorry guys, but as an inspector I will have to overrule all of you and say, NO!
Capitol NO, I m pretty sure!!300.15 Boxes, Conduit Bodies, or Fittings ? Where Required.johnny watt said:Is it acceptable to come out of the meter channel with conduit into an LB that will be buried below the final grade by a few inches?
I could have access to it in less then a minute with a shovel if ever need be.
I want to go through the rim joist and this is the rare time that the rim joist is below grade.
A sweep would not do as neat of a job.
wasasparky said:There you go, another inspector failing something with no code reference.![]()
Inspectorcliff said:Capitol NO, I m pretty sure!!300.15 Boxes, Conduit Bodies, or Fittings ? Where Required.
A box shall be installed at each outlet and switch point for concealed knob-and-tube wiring.
Fittings and connectors shall be used only with the specific wiring methods for which they are designed and listed.
Where the wiring method is conduit, tubing, Type AC cable, Type MC cable, Type MI cable, nonmetallic-sheathed cable, or other cables, a box or conduit body shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A) through (M).
(A) Wiring Methods with Interior Access. A box or conduit body shall not be required for each splice, junction, switch, pull, termination, or outlet points in wiring methods with removable covers, such as wireways, multioutlet assemblies, auxiliary gutters, and surface raceways. The covers shall be accessible after installation.
johnny watt said:Is it acceptable to come out of the meter channel with conduit into an LB that will be buried below the final grade by a few inches?
I could have access to it in less then a minute with a shovel if ever need be.
I want to go through the rim joist and this is the rare time that the rim joist is below grade.
A sweep would not do as neat of a job.
I'll bets he is from Texas? Whom else would get their conduilttes mixed with them LBJ not to be mixed with their L.B. fittings. and such.weressl said:Only LBJ, but he is already there.....:grin:
Did anyone say; heck no?
Inspectorcliff said:I'll bets he is from Texas? Whom else would get their conduilttes mixed with them LBJ not to be mixed with their L.B. fittings. and such.
I was refering to the corrosion of the srews an the LB itself and duct seal if he was going to use rocks,I agree this is not applicacal. But I might still be wrong on the referance, Always willing to learn.:wink:benaround said:James, An LB below grade would not be" judged suitible for the conditions",
no more than it would be if in concrete. IMO, 344.10 does not support this
installation.