I said no, because to me, "...through framing members..." means, holes, not laying on top of framing members,
I'm invoking Charlie's Rule on you! ...........
If we are all talking about the same thing, these are usually top load joists or trusses and you cannot hang anything or lay anything on the bottom cord without the approval of the engineer.
OUCH! Red tagged from left field.
We get on some jobs that follow that for everything but on most of our jobs 1/2" through 1.25" are routinely supported by the bottom cord.
And the OP did not use the word "series" in that context either.I never applied the word 'series' to the framing itself, but rather the direction of the EMT in relationship to the direction of the framing.
And the OP did not use the word "series" in that context either.
I agree with you. Looking more closely at the wording.358.30 Securing and supporting. EMT shall be installed as a complete system in accordance with 300.18 and shall be securely fastened in place and supported in accordance with 358.30(A) AND (B).
I agree with you. Looking more closely at the wording.
They are saying, securely fastened in accordance with 358.30(A), since this is the paragraph that speaks about things being fastened, AND supported in accordance with 358.30(B), since this is the paragraph that speaks about things being supported. (B) is not an exception to (A), so you have to fasten every 10 feet. If, for example, the floor joists are 2 feet apart, then you can put the EMT through holes in the joists, but you have to securely fasten the EMT to the wood every fifth joist board.
- Securely fastened in place AND supported . . . .
- . . . in accordance with 358.30(A) AND (B).
I vote no.
The EMT is only required to be 'securely fastened' within 3' of box or conduit body, beyond that it only has to be supported when run through framing members. You cannot try to use A and B simultaneously.
This is the key to my disagreement with the majority, please elaborate.You cannot try to use A and B simultaneously.
Attached is one from the 2005 handbook (kudos to those who pointed that out.)cowboyjwc said:Have a picture?
As I see it, both "A" and "B" apply equally to the EMT, so therefore B's existence is fairly moot:
..anytime the Code says "AND" it means both (or all) conditions stated must be complied with.
This is the key to my disagreement with the majority, please elaborate.
As I see it, both "A" and "B" apply equally to the EMT, so therefore B's existence is fairly moot: as all conduits that are fastened will necessarily be supported in the process of fastening.
Attached is one from the 2005 handbook (kudos to those who pointed that out.)
In the handbook, it refers you back from the EMT article. Nice try.The picture from the handbook references IMC, not EMT. So it is non-compliant. So far the minority is correct....:grin:
Of course that is supposed to be true.
In this case I can't explain it other than IMPO it is an error. See my answer to George about why I feel it is an error.
My opinion remains the same, compliant.