"Q 3. When EMT is installed within metal studs and it is not resting on the bottom of the opening, is additional support required?
A 3. Horizontal runs of EMT is considered supported by openings through framing members where securely fastened within 3 ft of termination points [358.30(B)]. The key word here is "supported". If the raceway is not resting on the framing member, then it is not supported. This does not mean that the conduit must rest on every framing member. As long as it is resting on one framing member every 10' and it is securely fastened within 3' of the tubing termination points, the installation complies with the NEC. "
Has nothing to do with the situation of truss webs.
In a wall the emt can not move very far. Laying on a truss it could move far enough to become uncoupled at a coupling. They need support and secured.
But i am all for getting Mikes input on this post.
A 3. Horizontal runs of EMT is considered supported by openings through framing members where securely fastened within 3 ft of termination points [358.30(B)]. The key word here is "supported". If the raceway is not resting on the framing member, then it is not supported. This does not mean that the conduit must rest on every framing member. As long as it is resting on one framing member every 10' and it is securely fastened within 3' of the tubing termination points, the installation complies with the NEC. "
Has nothing to do with the situation of truss webs.
In a wall the emt can not move very far. Laying on a truss it could move far enough to become uncoupled at a coupling. They need support and secured.
But i am all for getting Mikes input on this post.