- Location
- Illinois
- Occupation
- retired electrician
I did not read your post correctlyThey don't agree with which part of my statement? They said that if the spacing cannot be maintained at the box then it must be protected. I said the same thing.
I did not read your post correctlyThey don't agree with which part of my statement? They said that if the spacing cannot be maintained at the box then it must be protected. I said the same thing.
Okay and thanks for posting that. I thought that they agreed with me but was surprised when you said that they didn't. It seems confirmed that the protection is required and that they won't accept an exception for where you enter a box.I did not read your post correctly
If it is in the Code, I would be hard pressed to not call a portion of this code and not others. When I start assuming that there may not be issues, and I know otherwise, then why have codes if only portions are called and nothing else in that realm and scheme of things. I always strive to be better at my profession, but I am finding others not so much.... You would think one wants to be better and call a code, leaving their own biased opinion out. Its seems this was looked at and opinions/exceptions were shot down, for good reason. If anyone is reading this throughout this Country, I would like to know who enforces this box protection , enforces the code as written, and welcome their opinion. Please message me privately if need be to avoid ridicule, I would greatly appreciate itI see you're talking about where the cable or raceway enters the box. I don't guess there's enough instances of damage to warrant a code requirement.
ANY cable in the 1.25" area needs to be protected including the several inches that you've mentioned.The only jurisdiction and inspector I have seen enforce this protection requires plates behind the box. What about the several inches of cable above or below the box?
Strictly by code yes but the jurisdiction requiring the protection asks for a 4sq blank behind the box. This only protects the wires in the box.ANY cable in the 1.25" area needs to be protected including the several inches that you've mentioned.
If the 4" square isn't big enough then you'll need two or three of them or a bigger nail plate.Strictly by code yes but the jurisdiction requiring the protection asks for a 4sq blank behind the box. This only protects the wires in the box.
Colorado does. I was one. Electrical inspections are now required to be done by licensed electricians, though.In Souther California, they have "Combination Inspector", do other jurisdictions use them ?
Hi Curt, first of all , thank you for your input. When I was inspecting I made sure that when they came out of the box turned up into the center of stud to get the 1 1/4 from framing member edge.. or protected, to include the box.As I mentioned previously, In my over 40 in the trade I have never seen wiring damaged either directly before or inside the box. I have seen may damaged wires inside wall from shear nails and long screws.
Yes codes should be followed but there also needs to be common sense.
The only jurisdiction and inspector I have seen enforce this protection requires plates behind the box. What about the several inches of cable above or below the box?
Also may GC's remove the plates behind switch boxes after inspection. They cause a bump in the drywall that creates issues with the door jamb casing.
Thank you for the reply, and appreciate you inputColorado does. I was one. Electrical inspections are now required to be done by licensed electricians, though.
Ron
combination inspectors ?In Souther California, they have "Combination Inspector", do other jurisdictions use them ?
Building, plumbing, electrical, HVAC, etc.....combination inspectors ?
Hi Ron, Electrical inspections from a City or County jurisdiction has to be done by a licensed electrician ? Or a licensed electrician brought up through the trade and hired on as an inspector that is able to do the electrical inspections for the City ? But has to have an electrical background to perform electrical inspections.....I heard that Boise Idaho requires and inspector to have a plumbing background to look at plumbing, and unless the inspector has that back ground, then he or she may not be able to perform the plumbing inspection....Colorado does. I was one. Electrical inspections are now required to be done by licensed electricians, though.
Ron
Agree, but then again, the Verbiage is already written into the code. It just gets overlooked. I agree more emphasis and spending time in training on this topic would go along way... When I used to go to the training, it was great taking the courses that knowledgeable instructors taught, and the in class questions and feedback from the instructors and individuals in the class. Great teaching and learning on how others interpret the code. Kind of like this topic here.You need to understand the way code rules and their wording are put into the actual code. It takes a Public Input with substantiation.
For instance, the requirement for all commercial kitchen GFCI's came about due to casualties which was the substantiation for the ROP (PI now).
I agree with infinity that the current wording does cover it but if so many are not enforcing it it might be a good time to submit a PI with specific wording.
A licensed electrician is hired by a city, county, state or private inspection agency. That electrician should be a journeyman at a minimum.Hi Ron, Electrical inspections from a City or County jurisdiction has to be done by a licensed electrician ? Or a licensed electrician brought up through the trade and hired on as an inspector that is able to do the electrical inspections for the City ? But has to have an electrical background to perform electrical inspections.....I heard that Boise Idaho requires and inspector to have a plumbing background to look at plumbing, and unless the inspector has that back ground, then he or she may not be able to perform the plumbing inspection....
That is why I am on this great site and only want consistency with our profession, and above all , others opinions on this or what they are doing. It is wrong for an Inspector to look the other way or not enforce a required Code because in his opinion he doesn't think it to be a problem, or has always missed it..... It is what I am experiencing now