C.E.C 300.4 Protection against Physical Damage.

Merry Christmas

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
I've thought about this many times, but just figured the inspector knew that it was impossible to maintain the 1.25" clearance required. I always took my cables after stapling and pulled them to the center, minimizing the length of Romex that was within the 1.25". I guess if I had an inspector that was enforcing this, I would just scab a short piece of 2x4 onto the original framing member and put my box to that. Then my argument would be that my box is even 1.5" away from the original framing member. It would be a pain to do that for every box, but the scrap pieces of 2x4's are plentiful around the site.
 
Location
Modesto, Ca
Occupation
Retired Building Inspector
I've thought about this many times, but just figured the inspector knew that it was impossible to maintain the 1.25" clearance required. I always took my cables after stapling and pulled them to the center, minimizing the length of Romex that was within the 1.25". I guess if I had an inspector that was enforcing this, I would just scab a short piece of 2x4 onto the original framing member and put my box to that. Then my argument would be that my box is even 1.5" away from the original framing member. It would be a pain to do that for every box, but the scrap pieces of 2x4's are plentiful around the site.
Totally agree, but then who would install the small piece of 2 x framing to move away ? The electrician ? Framers ? Then the location and we know that electrical boxes sometimes get moved or relocated....
 
Location
Modesto, Ca
Occupation
Retired Building Inspector
It’s interesting that there is nothing commercially available for this situation……..
There actually is a product out there designed exclusively for this protection. It's called the EBP-1 and manufactured by Metal Products Company out of Oregon. They are kind of like Simpson. I will try to see if I can get hold of one and post it here.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Totally agree, but then who would install the small piece of 2 x framing to move away ? The electrician ? Framers ? Then the location and we know that electrical boxes sometimes get moved or relocated....
I have nailed or screwed up plenty of spacer blocks. Carpentry is part of our work.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor

 

Greentagger

Senior Member
Location
Texas
Occupation
Master Electrician, Electrical Inspector
It’s interesting that there is nothing commercially available for this situation……..
There actually is a product called a stacker which secures several NM cables running up parallel with framing member. Maybe not exactly the protection part this post is referencing but protection not needed as stacker keeps multiple cables more than 1 1/4” from edge of framing member.
 

Seven-Delta-FortyOne

Goin’ Down In Flames........
Location
Humboldt
Occupation
EC and GC


Great. Now I’ve found another part I need to stock on the already overstuffed service body. 🙄

Thanks a lot, Larry! 🙄😂😂👍
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
Totally agree, but then who would install the small piece of 2 x framing to move away ? The electrician ? Framers ? Then the location and we know that electrical boxes sometimes get moved or relocated....
The electrician installs the small pieces of 2x4's prior to installing the box. There are scrap pieces laying around. Now, any wiring is 1.5" away from the original framing member that the sheetrockers are going to screw to. An 1 1/2" usually won't make a difference on switch and gen. purpose receptacles. If over a countertop, well, you need to be able to read a scale ruler to determine which side you need to scab onto to keep your spacing requirements.
 
Location
Modesto, Ca
Occupation
Retired Building Inspector
Larry, I think the OP is referring to the cables entering the openings in the boxes. They are always going to be further back, making your cables being much less than 1.25" from the framing members. Those cable stackers are awesome when you have multi-gang boxes and several cables.
Totally agree. This is why I posted this to see actually what folks are doing. It is in the code to protect. When I was an inspector I always call this section of the code, when I saw wiring closer then the 1.25 space. It was mostly at the bores, top plates, bottom plates, ETC...But the location is no different at the back of the boxes. I missed it also. Its required, but most miss it or look past it, ignore it or just completely turn a blind eye. I am sure many on this thread, protect bored holes and other locations but just miss the back of boxes. I have one electrical contractor that I know state " Yes it is required...but nobody does it ". Then, you have the wiring inside the box all made up and I have seen a lot of wiring made up in a box completely pushed up against the back and not meeting the 1.25 distance. The 300.4 is code and was written into it for a reason... I know people do not want to do extra work or buck the trend, or give reasons for why they don't protect.
 
Location
Modesto, Ca
Occupation
Retired Building Inspector
Larry, I think the OP is referring to the cables entering the openings in the boxes. They are always going to be further back, making your cables being much less than 1.25" from the framing members. Those cable stackers are awesome when you have multi-gang boxes and several cables.
Those stackers or clips work great but after they leave or enter the back of the box, but that location is still in violation of 300.4 where they enter. I have seen them within a 1/4" to framing member edge.
 
Location
Modesto, Ca
Occupation
Retired Building Inspector
Here is the EBP-1 that I have installed in my houses prior to rock and even Lath install. They are so easy and just push in and done, some with the bigger boxes have a screw hole attachment. These protection brackets work great.
 

Attachments

  • IMG_6316.jpg
    IMG_6316.jpg
    492.8 KB · Views: 7
Location
Modesto, Ca
Occupation
Retired Building Inspector

Yes, that is the same company that produces the box protector. They are new to producing the EBP-1.... But same company. Those plates work fine but attached to the stud face and usually get removed from the sheet rock/planers, because of the hump on the framing member. And when they remove them to plane the stud, they never put them back on...
 
Location
Modesto, Ca
Occupation
Retired Building Inspector