Cabinet entry - Code violation ?

Status
Not open for further replies.

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
I'll be upgrading an electrical service in the next week or so. The current breaker panel is flushed into a wall in a finished area of a basement. Apparently, over the years, the only way to add circuits to this panel was to run a PVC up the side of the house to the attic and enter the cabinet through the back (not necessarily through factory made knock-outs). My new panel will have to accommodate these cabinet entries as they come down in specific areas of the siding.

Are the current panel entries in violation ? Can I install my new breaker panel to accommodate these existing conduits or will I have to make some type of corrections before I install ?

Suggestions are welcome. Code references would be appreciated. AHJ is currently out of town.

Thanks in advance,

Phil
Gold Star Electric
New Jersey
 
As long as the new entries are made to accommodate a connector (in otherwords use a knock out set or hole saw) and they do not interfere with the panel interior or mounting of the panel interior, all should be fine.

Roger
 
roger said:
As long as the new entries are made to accommodate a connector (in otherwords use a knock out set or hole saw) and they do not interfere with the panel interior or mounting of the panel interior, all should be fine.

Roger

I agree with Roger, but I actually saw a electrical contractor cutting out 4" KO's with a sawzall once. Panelboards are permitted to be field punched for conduit entries.
 