I have an application with 1000A continuous load with the conductors installed on a cable tray. So to support 1000A continuous, I need a 1250A CB. Based on 392.80(A)(2)(a), the ampacity shall not exceed 75% of ampacities listed in 310.15(B)(17). Using 90C column (assuming I could utilize 90C if insulation is rated for 90C), 700kcmil is rated for 850A. (At this point I would apply temperature derating if I have to, and check against 1000A load I am trying to support). Two sets are good for 2x850x.75=1,275A. Since the cable will be terminated at the CB with 75C rating, I take 75C column rating and compare it to CB rating: 755x2=1510 which is greater then the CB rating so I should be OK.
My question is how 110.14 applies to this. Based on 110.14, I need to use 310.15(B)(16) 75C rating instead of 310.15(B)(17) 75C rating for the last step above which doesn't make any sense to me.
thanks in advance