Cable Size
Note the south wire "commercial mode" calculator allows power factor to be entered and defaults to .9
Even when I enter a power factor of 1, I get significantly larger voltage drop results with Southwire's tool, than I get with Chapter 9 Table 9 data.
You can start with a power factor of 1 at the source, but it will deviate from a perfect 1, due to the fact that the impedance of the wire isn't pure resistance only. I'm inferring that Southwire is likely considering this effect, which increases the amount of vector voltage difference, above what the difference between voltage magnitudes alone would be.
Yes the total load is the same per post #16, 79.52 amps. You stated no more than 5% VD, 208*5%=10.4 volts maximum for both sections of the run combined.
Why would the total run be allowed to have 10v voltage drop if the max we are only allowed is 5%? I know its because of the splice but I don't get the logic.