Seven-Delta-FortyOne
Goin’ Down In Flames........
- Humboldt
- EC and GC
Or the fact that Southwire is in the business of selling product.
Or that……
240.4(B) permits you to use 4AWG copper on a 100 amp breaker for that load.So I'm here's a other twist.
You have calculated load of 79a but breaker feeding the load is 100a wire has to be sized for 100a and not 80a?
#4 THHN 85 amps, next size up 90 amps?240.4(B) permits you to use 4AWG copper on a 100 amp breaker for that load.
Now I'm really confused and were getting ready to start work ..lol. again it's AL SER cable.240.4(B) permits you to use 4AWG copper on a 100 amp breaker for that load.
I think that Don meant a 90 amp breaker not 100 amp.Breakers is 100a and calculated load is 80a. How would #4 be ok?
Can someone tell me if accurate?So lastly when doing a VD calc with a SPLICE BON in the run would I?
1. Input the calculated load at the end of the run only for the footage from source to splice box and then another calc with end of run calculated load from splice box to load?
See post #8. SER cable cannot be installed in underground conduit. 2017 NEC 338.12(A)(2).Now I'm really confused and were getting ready to start work ..lol. again it's AL SER cable.
Yes you do two separate calculations as if there are two separate runs.Can someone tell me if accurate?
It was never stated that the run is underground. In fact he said that it is not underground.See post #8. SER cable cannot be installed in underground conduit. 2017 NEC 338.12(A)(2).
What are you talking about? The scr cable will be installed over head outside of conduitSee post #8. SER cable cannot be installed in underground conduit. 2017 NEC 338.12(A)(2).
Single phaseIs this single phase or 3 phase? I am not getting your #s to match up.
The wire above is calculated as 3 phase but I see no /1.73 in your load calculations
So ..because I really need to know.lol. if the run is 490' and the calculated load is 79 amps( not taking into account the ocpd feeding the load..for now) and the splice box is located at the 290' mark of a 490' total run.Yes you do two separate calculations as if there are two separate runs.
We figured 3/0 for a portion of the run( to the splice box)and 1/0 for the remaining. I'm really hoping this works. We HAVE to install a splice box per the customerIf I did my math correctly using the 4/0 to a splice and then 1/o would exceed your 5% limit,
You are better off with 4/0 all the way.
and, as infinity noted, the cost of material and labor with the splice would not be worth the effort.
This is what I believe Southwire's calculator is doing behind the scenes.Or the fact that Southwire is in the business of selling product.
Yes the total load is the same per post #16, 79.52 amps. You stated no more than 5% VD, 208*5%=10.4 volts maximum for both sections of the run combined.1. I can do a voltage drop calc using the calculated load to the splice box(290'). Then do my second voltage drop calc using the same calculated load from the splice box to the load?
Note the south wire "commercial mode" calculator allows power factor to be entered and defaults to .9This is what I believe Southwire's calculator is doing behind the scenes.
What we'd calculate with the NEC's effecitve resistance values in Chapter 9/Table 9, would be (|green| - |blue|)/|green|
What Southwire's tool is calculating, is |red|/|green|. While technically a form of voltage drop, it's not the voltage drop we most commonly care about.