Cable Size
240.4(B) permits you to use 4AWG copper on a 100 amp breaker for that load.
Now I'm really confused and were getting ready to start work ..lol. again it's AL SER cable.
Breakers is 100a and calculated load is 80a. How would #4 be ok?
Doesn't the breaker need to protect wire so the wire ampacity should be equal or above breaker size ?
If I did my math correctly using the 4/0 to a splice and then 1/o would exceed your 5% limit,
You are better off with 4/0 all the way.
and, as infinity noted, the cost of material and labor with the splice would not be worth the effort.
Yes you do two separate calculations as if there are two separate runs.
So ..because I really need to know.lol. if the run is 490' and the calculated load is 79 amps( not taking into account the ocpd feeding the load..for now) and the splice box is located at the 290' mark of a 490' total run.
1. I can do a voltage drop calc using the calculated load to the splice box(290'). Then do my second voltage drop calc using the same calculated load from the splice box to the load?
Thanks
We figured 3/0 for a portion of the run( to the splice box)and 1/0 for the remaining. I'm really hoping this works. We HAVE to install a splice box per the customer
Or the fact that Southwire is in the business of selling product.
This is what I believe Southwire's calculator is doing behind the scenes.
What we'd calculate with the NEC's effecitve resistance values in Chapter 9/Table 9, would be (|green| - |blue|)/|green|
What Southwire's tool is calculating, is |red|/|green|. While technically a form of voltage drop, it's not the voltage drop we most commonly care about.
This is what southwi1000000064.pngre vd calculator is bringing back
Yes the total load is the same per post #16, 79.52 amps. You stated no more than 5% VD, 208*5%=10.4 volts maximum for both sections of the run combined.
Note the south wire "commercial mode" calculator allows power factor to be entered and defaults to .9