Re: Cable ties for MC cable
Ben, TURN YOUR CAPS OFF.
Now inline with Bobs post (AND IF YOU STICK AROUND YOU WILL INDEED SEE BOB NEVER GUESSES)
Let's start with 90.4,
The authority having jurisdiction for enforcement of of the Code has the responsibility for making interpretations of the rules, for deciding on the approval of equipment and materials, ...
This specifically allows an inspector to approve an installation on his judgement, regardless of the absence of a listing as long as the items in the installation are not specificaly required to be listed in an article.
Now 90.7, Note the second and third words, Specific items, these items are stated in the applicable articles, and relieves the AHJ of having to judge an item safe.
Now, look at this wording
--------------------------------------------------------------------------------
if the equipment has been listed by a qualified electrical testing laboratory that is recognized as having the facilities described above ...
--------------------------------------------------------------------------------
this would also relieve the inspector of this decision if a "non specific item" is listed.
With the exception of the items called for to be listed in the specific articles, there is no mandatory rule that requires all items to be third party tested.
Roger