mbrooke
Batteries Included
- United States
- Technician
Since the other T-line is not in the same ROW then no mutuals should factor.
Question, how much does the mutual coupling vary between lines in the same right of way vs 2 circuits on the same tower? Or 345kv and 115kv on the same tower? Just gauge my understanding.
They other parameters that are need to estimate the line impedance are:
1.) What type of static wire is being used and how many (1 or 2)?
2 static wires.
2.) What is the avg structure height from the ground up (don't include 10%+2' embedment)?
80 feet
3.) What is the physical spacing of the conductors with respect to the CL of the structure and the top of the structure?
CL? Let me double check the specs.
4.) Give me an idea of the soil impedance (or soil type).
Errrr... Id say clay soil? Certainly not an erade region.
5.) Lastly, can you provide more info on the T-Line length? If you have to give the structure spans (str. by str.), that is good. For a ~14 mile line, a difference of 1.4 miles is 10% error (0.7 mile = 5%) and is considered too much of an error. 10% error could easily cause an over or under trip event, result in mis-coordination, or simply fail to adequately protect the line.
So the exact length is needed here? Let me get it, for this line it is indeed very close to 14 miles.