Calculating Phase Currents for Unbalanced Loads

Status
Not open for further replies.

jghrist

Senior Member
If the phase currents are not separated by 120 degrees, there is no unique solution if we have only the line currents.
I think the criteria for no unique solution is if the delta load currents do not sum to zero (zero-sequence current <> 0).
 

Smart $

Esteemed Member
Location
Ohio
Well, double check me on this...but if I had a system with Vab=208<-30, Vbc=208<-150 and Vca=208<90 and between A-B, I connect an inductive impedance of 15.969<6.9, between B-C, I connect a capacitive impedance of 19.941<-18.56, and between C-A, I connect an inductive impedance of 28.139<13.74. My phase currents should be:

Iab=13.025<-36.9
Ibc=10.431<-131.44
Ica=7.392<76.26

In rectangular form:

Iab=10.416-j7.820
Ibc=-6.904-j7.820
Ica= 1.756+j7.180

Iab+Ibc+Ica = 5.268-j8.460 = 9.97<-58.09

Since Ia=Iab-Ica, Ib=Ibc-Iab & Ic=Ica-Ibc, we get

Ia=8.660-j15.000
Ib=-17.320+j0.00
Ic=8.660+j15.000

Ia+Ib+Ic= 0+j0 = 0

This is an unbalanced (and unequal power factor) delta connected loads, where the sum of the line currents equals zero, but the sum of the phase currents does not.
Well I didn't double check but your math appears good (I'm not getting any bad vibes ;)). But this makes my [disguised] point... Doesn't the circuit described have circulating current? i.e. there will be energy (which requires current) passed back and forth between the capacitive and inductive elements as long as the load is energized, and that energy is only dissipated upon deenergization of the circuit. That energy comes in on the lines during the first [few?] cycle upon energizing... which we don't discuss, because our modus operandi is after steady operating state has been achieved. I guess this takes us to jghrist last posed and unanswered question...???

I say if we are starting with a nominally-balanced delta load and trying to determine the initial stage of winding degradation, for example, the centroid solution or the p&n sequences method would suffice. The goal is not one which requires accuracy, but rather a dependable means to determine a moderate degree of unbalance beyond nominal in real-time. But then we have to ask, would not just the line values themselves suffice for such a determination?
 

rattus

Senior Member
Or, a simpler example:

Vab=208<-30, Vbc=208<-150 and Vca=208<90 and between A-B, I connect a 10 ohm resistor. B-C and C-A are open. Iab = 20.8<-30. Ibc=Ica=0
Iab+Ibc+Ica=Iab=20.8<-30 not =0

Ia=20.8<-30, Ib=20.8<150, Ic=0, Ia+Ib+Ic=0

Intuition leads me to believe the load currents sum to zero, but logic says otherwise. Clearly, changing one of the load impedances changes that current only and does not affect the other two. That is, tweaking one load would change the sum of the load currents
 

rattus

Senior Member
Or, a simpler example:

Vab=208<-30, Vbc=208<-150 and Vca=208<90 and between A-B, I connect a 10 ohm resistor. B-C and C-A are open. Iab = 20.8<-30. Ibc=Ica=0
Iab+Ibc+Ica=Iab=20.8<-30 not =0

Ia=20.8<-30, Ib=20.8<150, Ic=0, Ia+Ib+Ic=0

Intuition leads me to believe the load currents sum to zero, but logic says otherwise. Clearly, changing one of the load impedances changes that current only and does not affect the other two. That is, tweaking one load would change the sum of the load currents
 

jghrist

Senior Member
Or, a simpler example:

Vab=208<-30, Vbc=208<-150 and Vca=208<90 and between A-B, I connect a 10 ohm resistor. B-C and C-A are open. Iab = 20.8<-30. Ibc=Ica=0
Iab+Ibc+Ica=Iab=20.8<-30 not =0

Ia=20.8<-30, Ib=20.8<150, Ic=0, Ia+Ib+Ic=0
And to answer the question about load currents being 120? apart, just add 10 kohm resistors in B-C and C-A. Then these load currents will be 20.8 mA, all power factors the same, all currents 120? apart, but the sum of the currents is still very close to 20.8<-30.:cool:
 
Status
Not open for further replies.