Calculating Phase Currents for Unbalanced Loads
Anyway, I came up with the following formulas and need someone to verify them...
New formulas. Verified myself on one example (CAD, graphical). Could use additional verification from others :D
All,
Sorry for late reply here is some measured data for you to play with, .txt file.
The sampling rate is 5kHz, the supply freq. is 50Hz.
Voltages are line-to-neutral (volts), currents are line (amps).
I will try and get my head around the latest few posts then get back to you.
Using a 100 samples/cycle cosine filter and using the va angle as a reference, I get the line currents to be:
ILa = 21.84 @ -39.66?
ILb = 23.15 @ -157.32?
ILc = 23.19 @ 78.73?
Using sequence components and assuming no circulating load current (no zero-sequence), I get the delta load currents to be:
IDab = 12.83 @ -7.48?
IDbc = 13.64 @ -129.26?
IDca = 12.89 @ 108.5?
You have to have at least 1-1/4 cycles of data to use a cosine filter, so I duplicated the values to get 2 identical cycles.
Using the equations for 4 samples per cycle on the 75th and 100th samples, I get slightly different values of line current (again referenced to Va angle):
ILa = 21.62 @ -40.08?
ILb = 23.15 @ -159.25?
ILc = 23.22 @ 78.71?
Smart, your new set of equations look too good to be true! Are they for instantaneous values? Please can you list the assumptions you made in getting to them?
JGChrist, please can you explain how you used sequence components to transform from line to delta quantities?
It works with your numerical example in Posts 53-56. How was it derived?
Derived geometrically...
Given three delta currents of any magnitude and angle, the only requirement (KCL) is the currents add to zero.
The Va vector is not necessary. It is only there for visual referrence.
Now that we have the three delta current vectors, we arrange them in pairs, tail to head (reversing direction as needed) to add them to get line current vectors.
In doing the above, I noticed there is a gemoetric equivalent vector across the heads of the base delta vectors. Note the parallelograms.
So we can actually draw it up as such...
Here I accidentally closed my graphics program and lost the drawing, so I'll try to expain the rest without visual aid :mad:
In the last image, if we extended the delta current vectors' tails, they fall on the midpoints of the line current vectors. Through analysis it can be determined the required extension is equal to 1/2 the delta leg's current magnitude. This creates multiple triangles with common sides and angles with three known magnitudes. This is enough info to determine the unknowns using the law of cosines to solve for each delta leg's current magnitude.
W, it can be used for instantaneous values but there are some considerations. One, the accuracy is dependent in part on the three values adding to zero. I noticed your sample data consistently does not, but resonably close to a zero total. Two, the result is always positive. A plot of the result will appear as if an ABS function was applied to sine waveform data (plotted appears similar to rectified sinewave current). Third, for some imbalanced data near zero crossings, the value under the square root function will be negative, yielding an indeterminate result.
Your solution uses the magnitude of the current vectors. Instantaneous values are not the magnitudes of the vectors, but are the values of points along the sinusoid. Using your Post #53 example instantaneous values in your equation would give:
IAB = 4.413, IBC = 1.085, ICA = 5.498
instead of the actual
IAB = 4.267, IBC = 5.511, ICA = 4.648
Instantaneous values are magnitudes... and they have an angle too. Consider the difference between phasors and vectors... the former being dynamic versus the latter being static.
That said, it amounts to instantaneous input to the formulas yields instantaneous output... rms input yields rms output, and magnitude only in both cases.
Here's some waveforms of the instantaneous. In this first one, the top chart is of the values as calculated using ideal input (pure sinusoids, equal magnitudes, equal power factors). In the lower chart I added a polarity factor to the equation: Ia-Ib / |Ia-Ib| for Iab polarity, and shifted appropriately for the other two.
Below is what happens when I slightly imbalance the magnitudes and power factors...
...and if I use W's data, first let's look at the line current plot...
...and here's the plot of delta currents... and remember, the line current values do not add up to zero...
The magnitudes all have to be divided by sqrt(2) to get rms values.
I have implemented the equations (supplied by Smart) in MATLAB - they are attached since I don't know how to put them in the text :confused:
The code I used is given below:
% WyeDelta.m
% Transforms the measured line currents into
% phase currents for delta connected load
function [ia ib ic] = WyeDelta(i1,i2,i3)
ia = abs(sqrt( 2*(i1).^2 + 2*(i2).^2 - (i3).^2) / 3);
ib = abs(sqrt( 2*(i2).^2 + 2*(i3).^2 - (i1).^2) / 3);
ic = abs(sqrt( 2*(i3).^2 + 2*(i1).^2 - (i2).^2) / 3);
% Calculate the polarity
ia_pol = (i1-i2)./abs(i1 - i2);
ib_pol = (i2-i3)./abs(i2 - i3);
ic_pol = (i3-i1)./abs(i3 - i1);
% Correct the polarity
ia = ia.*ia_pol;
ib = ib.*ib_pol;
ic = ic.*ic_pol;
end
I added the 'abs' function to remove the imaginary components introduced due to the -ve square roots.
They seem to be fairly good except at the point of polarity change.
Thanks for posting your plots - it helped with my understanding.
I have another question: I want to analyse the negative sequence current in the delta load, at the moment I am applying the symmetrical component transform to the instantaneous data by applying a phase shifts in MATLAB. Would it be okay just to use a set of calculated phasors then apply the symmetrical components transform to the phasors?
If I remove 'abs' and repalce it with 'real' (takes only the real part of the sqrt) then I get a plot similar to Smart's.
See attached.
/QUOTE]
Smart, that is not right.
Instantaneous values are real numbers which may be positive or negative and are functions of time with the phase angle being part of the trig argument but not part of the value. e.g.,
v(t) = Vp*cos(wt + phi)
Just ask Bes!
Magnitudes, by definition, are always positive and constant and may be peak values or RMS values of a voltage or current sinusoid.
Vectors have a magnitude and direction in space, e.g. as in an electric field.
Phasors have a magnitude and phase angle which is really a measure of time.
The value of a static phasor is a complex number which may be expressed in polar form as
Vrms @ phi
A rotating phasor is expressed as,
Vp[cos(wt + phi) + jsin(wt + phi)]
Its value is a complex number which is a function of time and does not carry a phase angle which is part of the trig arguments.
/QUOTE]
Just ask Bes!
Vrms @ phi
Hmm... in the grand picture of conventional electrical math, that is of course correct... but you're missing the context of my statement.
You have instant values of Ia, Ib, and Ic. They occur at a point in the time of a cycle, which has an angle associated with it. Now even with that true, let's set it aside for a moment...
We have three lines feeding a 3? delta load. In the same manner in which the loads are connected, the instant values are connected. Though they are just values, they must sum to zero.
In graphical terms, that means a line connected to another line at one of their endpoints and their other endpoints are bridged by connecting to a third line's endpoints. That forms a triangle. As such they form angles relative to each other, but they are angles nonetheless. And because this is planar geometry, the lines also have direction relative to each other. If one continues to pursue the issue, I'm fairly certain correltaion to other angles and directions regarding the matter are possible.
So when it is all said and done, you can stick with the conventional sense... or not. You can be right and wrong either way... or from my viewpoint, totally right ;)
...which brings to mind something I was once told and recall when pertinent: The difference between right and wrong is merely what we think... :D
Food for thought, what is the difference between instant values and instantaneous values...???
One is a noun and the other is an adjective. e.g., an instantaneous value is the value of the function at a given instant.
And for that matter, I see no need to bring instantaneous values into a steady state problem. And, conventions are established to help us understand each other. If you insist on being unconventional, one might think you don"t know what you are talking about.
Now, down to business. I agree with your last diagram, but you surely took a roundabout way to get there. Clearly, the equations for Ia, Ib, and Ic boil down to the sum and difference of the phase current phasors. But, that is of no importance.
What is important is your statement that the extensions of the phase current phasors intersect the line current phasors at their midpoints. That may be true, but can you verify that mathematically or through a reference?
... If you insist on being unconventional, one might think you don"t know what you are talking about.
If everyone was conventional, there'd be no discoveries. I am knowledgeable about conventional ways, but I do not subscribe to those ways incessantly... and if a person thinks I don't know what I'm talking about, it is not I they should be analyzing. I seldom talk about anything which I do not know, at least to some degree, and seldom stretch that degree beyond my belief that I know what I'm talking about... and that is to say I may not know what I'm talking about but only to the degree I believe I know what I'm talking about.
With that said, why would I care whether someone I don't know or care about thinks I don't know what I'm talking about?
Do you know what I'm talking about? ;):D;):D
So, are you going to back that statement up with the not roundabout way?
How about by both, math and reference... Note the equation at the top of the image below, then click here and refer to equation (4).
I can see from your reference and math that your equations for the delta load currents are correct if the neutral point of the delta currents is at the centroid of the triangle formed by the line currents.
Is there any proof that the neutral point is at the centroid? It is in at least one example, but is it always true?
My point exactly:
My point exactly:
That is my question also.
Smart$, this was really well done, but I don't think that it works. In post 66 you mention that the accuracy depends on the "values adding to zero." While this should be true for the line currents Ia+Ib+Ic=0, using the triangle centroid also means that is necessarily true for the phase currents too Iab+Ibc+Ica=0. I don't believe that this should be the case.
For instance, imagine a 208V, 3ph system with phase voltages of Vab=208<-60, Vbc=208<180 and Vca=208<60. If you connect a 2080W (resistive) load between A-B and a 1560W (resistive) load between B-C, and connect no load between C-A, then you would have phase currents of Iab=10<-60 and Ibc=7.5<180 and Ica=0
We know that Ia=Iab-Ica (etc) so, Ia=10<0, Ib=15.2<145.3 and Ic=7.5<0. If you add Ia+Ib+Ic, you will find that the sum is zero. However, if you add Iab+Ibc+Ica, you will find that the sum is 9<-106.1
If you took the line vectors and graphed them, and then used the centroid lines for the phase currents, you'd have a value for Ica which was not zero. But in the example, there is no load between C-A, so Ica must be zero. I don't think the triangle centroid method will provide the correct phase currents in all cases.