Ignore that request... I discovered an error or three :roll:...
Anyway, I came up with the following formulas and need someone to verify them...
Ignore that request... I discovered an error or three :roll:...
Anyway, I came up with the following formulas and need someone to verify them...
New formulas. Verified myself on one example (CAD, graphical). Could use additional verification from others...
Anyway, I came up with the following formulas and need someone to verify them...
It works with your numerical example in Posts 53-56. How was it derived?New formulas. Verified myself on one example (CAD, graphical). Could use additional verification from others
![]()
All,
Sorry for late reply here is some measured data for you to play with, .txt file.
The sampling rate is 5kHz, the supply freq. is 50Hz.
Voltages are line-to-neutral (volts), currents are line (amps).
I will try and get my head around the latest few posts then get back to you.
It works with your numerical example in Posts 53-56. How was it derived?
Derived geometrically...Smart, your new set of equations look too good to be true! Are they for instantaneous values? Please can you list the assumptions you made in getting to them?
...
Your solution uses the magnitude of the current vectors. Instantaneous values are not the magnitudes of the vectors, but are the values of points along the sinusoid. Using your Post #53 example instantaneous values in your equation would give:W, it can be used for instantaneous values but there are some considerations. One, the accuracy is dependent in part on the three values adding to zero. I noticed your sample data consistently does not, but resonably close to a zero total. Two, the result is always positive. A plot of the result will appear as if an ABS function was applied to sine waveform data (plotted appears similar to rectified sinewave current). Third, for some imbalanced data near zero crossings, the value under the square root function will be negative, yielding an indeterminate result.
Smart, your new set of equations look too good to be true! Are they for instantaneous values? Please can you list the assumptions you made in getting to them?
JGChrist, please can you explain how you used sequence components to transform from line to delta quantities?
Instantaneous values are magnitudes... and they have an angle too. Consider the difference between phasors and vectors... the former being dynamic versus the latter being static.Your solution uses the magnitude of the current vectors. Instantaneous values are not the magnitudes of the vectors, but are the values of points along the sinusoid. Using your Post #53 example instantaneous values in your equation would give:
IAB = 4.413, IBC = 1.085, ICA = 5.498
instead of the actual
IAB = 4.267, IBC = 5.511, ICA = 4.648
Using a 100 samples/cycle cosine filter and using the va angle as a reference, I get the line currents to be:
ILa = 21.84 @ -39.66?
ILb = 23.15 @ -157.32?
ILc = 23.19 @ 78.73?
Using sequence components and assuming no circulating load current (no zero-sequence), I get the delta load currents to be:
IDab = 12.83 @ -7.48?
IDbc = 13.64 @ -129.26?
IDca = 12.89 @ 108.5?
You have to have at least 1-1/4 cycles of data to use a cosine filter, so I duplicated the values to get 2 identical cycles.
Using the equations for 4 samples per cycle on the 75th and 100th samples, I get slightly different values of line current (again referenced to Va angle):
ILa = 21.62 @ -40.08?
ILb = 23.15 @ -159.25?
ILc = 23.22 @ 78.71?
Instantaneous values are magnitudes... and they have an angle too. Consider the difference between phasors and vectors... the former being dynamic versus the latter being static.
/QUOTE]
Smart, that is not right.
Instantaneous values are real numbers which may be positive or negative and are functions of time with the phase angle being part of the trig argument but not part of the value. e.g.,
v(t) = Vp*cos(wt + phi)
Just ask Bes!
Magnitudes, by definition, are always positive and constant and may be peak values or RMS values of a voltage or current sinusoid.
Vectors have a magnitude and direction in space, e.g. as in an electric field.
Phasors have a magnitude and phase angle which is really a measure of time.
The value of a static phasor is a complex number which may be expressed in polar form as
Vrms @ phi
A rotating phasor is expressed as,
Vp[cos(wt + phi) + jsin(wt + phi)]
Its value is a complex number which is a function of time and does not carry a phase angle which is part of the trig arguments.
Hmm... in the grand picture of conventional electrical math, that is of course correct... but you're missing the context of my statement.Instantaneous values are magnitudes... and they have an angle too. Consider the difference between phasors and vectors... the former being dynamic versus the latter being static.
/QUOTE]
Smart, that is not right.
Instantaneous values are real numbers which may be positive or negative and are functions of time with the phase angle being part of the trig argument but not part of the value. e.g.,
v(t) = Vp*cos(wt + phi)
Just ask Bes!
Magnitudes, by definition, are always positive and constant and may be peak values or RMS values of a voltage or current sinusoid.
Vectors have a magnitude and direction in space, e.g. as in an electric field.
Phasors have a magnitude and phase angle which is really a measure of time.
The value of a static phasor is a complex number which may be expressed in polar form as
Vrms @ phi
A rotating phasor is expressed as,
Vp[cos(wt + phi) + jsin(wt + phi)]
Its value is a complex number which is a function of time and does not carry a phase angle which is part of the trig arguments.
You have instant values of Ia, Ib, and Ic. They occur at a point in the time of a cycle, which has an angle associated with it. Now even with that true, let's set it aside for a moment...
We have three lines feeding a 3? delta load. In the same manner in which the loads are connected, the instant values are connected. Though they are just values, they must sum to zero.
In graphical terms, that means a line connected to another line at one of their endpoints and their other endpoints are bridged by connecting to a third line's endpoints. That forms a triangle. As such they form angles relative to each other, but they are angles nonetheless. And because this is planar geometry, the lines also have direction relative to each other. If one continues to pursue the issue, I'm fairly certain correltaion to other angles and directions regarding the matter are possible.
So when it is all said and done, you can stick with the conventional sense... or not. You can be right and wrong either way... or from my viewpoint, totally right
...which brings to mind something I was once told and recall when pertinent: The difference between right and wrong is merely what we think...
Food for thought, what is the difference between instant values and instantaneous values...???
Food for thought, what is the difference between instant values and instantaneous values...???
One is a noun and the other is an adjective. e.g., an instantaneous value is the value of the function at a given instant.
And for that matter, I see no need to bring instantaneous values into a steady state problem. And, conventions are established to help us understand each other. If you insist on being unconventional, one might think you don"t know what you are talking about.
Now, down to business. I agree with your last diagram, but you surely took a roundabout way to get there. Clearly, the equations for Ia, Ib, and Ic boil down to the sum and difference of the phase current phasors. But, that is of no importance.
What is important is your statement that the extensions of the phase current phasors intersect the line current phasors at their midpoints. That may be true, but can you verify that mathematically or through a reference?
If everyone was conventional, there'd be no discoveries. I am knowledgeable about conventional ways, but I do not subscribe to those ways incessantly... and if a person thinks I don't know what I'm talking about, it is not I they should be analyzing. I seldom talk about anything which I do not know, at least to some degree, and seldom stretch that degree beyond my belief that I know what I'm talking about... and that is to say I may not know what I'm talking about but only to the degree I believe I know what I'm talking about.... If you insist on being unconventional, one might think you don"t know what you are talking about.
With that said, why would I care whether someone I don't know or care about thinks I don't know what I'm talking about?
Do you know what I'm talking about?
So, are you going to back that statement up with the not roundabout way?Now, down to business. I agree with your last diagram, but you surely took a roundabout way to get there.
What is important is your statement that the extensions of the phase current phasors intersect the line current phasors at their midpoints. That may be true, but can you verify that mathematically or through a reference?
How about by both, math and reference... Note the equation at the top of the image below, then click here and refer to equation (4).
![]()
I can see from your reference and math that your equations for the delta load currents are correct if the neutral point of the delta currents is at the centroid of the triangle formed by the line currents.
Is there any proof that the neutral point is at the centroid? It is in at least one example, but is it always true?
So, are you going to back that statement up with the not roundabout way?
/QUOTE]
Yes. one can easily write,
Ia = Iab - Ica
Draw that expression as a phasor diagram to obtain 1/3 of your diagram. Repeat for Ib and Ic to get the other 2/3.
How about by both, math and reference... Note the equation at the top of the image below, then click here and refer to equation (4).
![]()