While (a) covers the wires running from the outlet to the luminaire )
I don't think this makes sense...210.19(A)(4) Ex 1 deals with branch circuit taps.
The branch circuit is all conductors from the final overcurrent protective device protect the circuit and the outlet(s). Beyond the "outlet" is no longer "branch circuit."