You can run an ungrounded system but it is a different setup and protection scheme. There are delta distribution systems but there are pros and cons for either setup.On single phase circuits your neutral simply becomes phase two, on 3 phase circuits you end up with 3 wires instead of 4. At least how I imagine it. But if you say so I'll take your word for it.
I doubt you would just let a multi-grounded system become an ungrounded system because it is not just a simple thing. You sure wouldn't mix the two.
The neutral doesn't just "simply" become a phase conductor. You have to change the insulation and the location on the pole for the neutral. Your system protection scheme will have to be completely changed. All of your arrestors will have to change. Any transformer connected wye will have to be changed. Any other equipment rated line-ground will have to be changed. I'm sure there is more but I'm not awake yet.