mivey
Senior Member
The OP was going to run a neutral, just no ground.What OP proposes does work. Might create some problems during abnormal conditions and some have mentioned codes being violated.
Unless you do switch the neutral with transfer switch you are going to have parallel path involving the EGC that was run with generator suppy circuit and the service neutrals/utility MGN. But if you don't run a neutral there is none to switch either.
I am in agreement with others in that one might be as well off to just buy another generator. Materials spent to go 600 feet will get you most of another generator or maybe even all of a cheap one from Harbor Freight.