Strathead
Senior Member
- Location
- Ocala, Florida, USA
- Occupation
- Electrician/Estimator/Project Manager/Superintendent
Wow this reminds me of an old short story about a woman who accidentally put salt in her tea. Everyone came up with ways to remove the salt until a kid cam along and asked why she didn't just pour a new cup.
Take a multimeter, do a voltage reading to ground on the line side of the breaker, and do voltage test on the load side of the breaker. If there is a difference there is a voltage drop.
Regarding old breaker, new breaker, like most contacts, breaker contacts are designed to swipe across each other when they open and close. This wiping action cleans the contact and creates a better connection. New contacts actually need to be cycled under load a few times to get optimum contact. It takes a lot of cycles to damage the surface of contacts to the point of making them bad. Sometimes though it doesn't hurt to cycle a breaker a few times to see if the natural cleaning axpect will correct the situation.
PS, I used to overhaul large fram circuit breakers for a living, so I am not speaking out my butt on this one. (for once):lol:
Take a multimeter, do a voltage reading to ground on the line side of the breaker, and do voltage test on the load side of the breaker. If there is a difference there is a voltage drop.
Regarding old breaker, new breaker, like most contacts, breaker contacts are designed to swipe across each other when they open and close. This wiping action cleans the contact and creates a better connection. New contacts actually need to be cycled under load a few times to get optimum contact. It takes a lot of cycles to damage the surface of contacts to the point of making them bad. Sometimes though it doesn't hurt to cycle a breaker a few times to see if the natural cleaning axpect will correct the situation.
PS, I used to overhaul large fram circuit breakers for a living, so I am not speaking out my butt on this one. (for once):lol: