There's been a little bit of a debate between coworkers in my office... Can an ac and a dc circuit share a ground point?
There's been a little bit of a debate between coworkers in my office... Can an ac and a dc circuit share a ground point?
There's been a little bit of a debate between coworkers in my office... Can an ac and a dc circuit share a ground point?
Why not? What would be the purpose of grounding DC?
I guess so but is the question about whether it is permitted by code?There's been a little bit of a debate between coworkers in my office... Can an ac and a dc circuit share a ground point?
Ignorant Brit strikes again........In at least one case (PV solar), AC and DC grounds are required to be connected to each other.
It is not uncommon to find grounded DC systems. If you don't ground the DC you need to use fuses in both the positive and negative, if you ground one side, you only need a fuse for the other leg.Ignorant Brit strikes again........
What would you ground on the DC side?
If the DC system is a grounded system, I don't know of any code compliant way to have the DC grounding system isolated from the AC grounding system.i not sure. a lifted N on the AC side could be hazardous to the DC side.
why would you not keep the AC and DC "gnd" isolated?
to me it sounds more like bonding AC egc to DC gnd (or vice versa). but why?
if the gnd side of bridge rectifier is tied to the chassis (for DC gnd purposes) do you typically see the AC egc wire feeding that DC power supply also tied to the chassis? if AC egc is on the chassis i usually see the DC gnd isolated to its internal circuitry. a quick check, take any cots 120/240 50/60hz dc power supply (metal case) and ohm from ac egc to the dc gnd terminal. i checking mine right now. my desktop 20lb dc ps has ac egc tied to chassis, the ac egc is not tied to dc gnd.
But what would you ground on the DC side?If the DC system is a grounded system, I don't know of any code compliant way to have the DC grounding system isolated from the AC grounding system.
But what would you ground on the DC side?
Yes. But what do you ground on the DC system?All grounds are ultimately tied together, you know, in the ground.
All grounds are ultimately tied together, you know, in the ground.
Well, as jaggedben said, a negatively grounded PV system, as the name implies, has its negative conductor tied to ground. I'm not as familiar with battery/inverter systems, but I'm pretty sure they have the negative battery terminal tied to ground as well.Yes. But what do you ground on the DC system?
but that just means "on the DC side". the common "gnd" for the DC circuits is the Neg side of DC source. i guess this is more about isolation and less about how the DC side is grounded.Well, as jaggedben said, a negatively grounded PV system, as the name implies, has its negative conductor tied to ground. I'm not as familiar with battery/inverter systems, but I'm pretty sure they have the negative battery terminal tied to ground as well.
In a negatively grounded PV system there is normally a grounding electrode at the inverter that is bonded to the service ground, and both the AC and DC grounds are tied to it, along with the EGC from the array and the rest of the gear. Is that what you are asking?but that just means "on the DC side". the common "gnd" for the DC circuits is the Neg side of DC source. i guess this is more about isolation and less about how the DC side is grounded.
is there NEC verbiage calling for the DC "gnd" (dc neg in this case) to be tied to AC egc ?