That flies in the face of every installation over-sized for voltage drop.
No it doesn't. I think you're thinking of it backwards. If a put #4 on a 30A breaker because of voltage drop, the 30A is protecting the #4 at its point of supply. If I put #10 on 50A breaker (ignoring motors, etc.) Then the 50A breaker is not protecting the #10 at its point of supply.