That is exactly my point.Correct me if I’m wrong but I think what @Dennis Alwon is driving at is the ability of the flex to carry fault current back to a wire type EGC (or pipe) to actually carry fault current back to the source. For example if there’s a 500’ run of 2” FMC, the NEC doesn’t permit it to be used as an EGC. However, if there’s a fault halfway through the run to the raceway then the FMC still needs to act like an EGC in a sense to carry fault current to the appropriate EGC. Comparing it to a piece of PVC in the middle of the run is a different animal, PVC isn’t conductive and won’t carry any current anywhere.
Well, for one thing, if the flex is bonded to an EGC at both ends then faupt current can travel on both directions on the flex.
You are still depending on the flex to carry the fault. I realize this is not an issue in real life situation- or, at least, I don't think it is, however why does the nec say that flex is not an equipment grounding conductor and yet they expect it to carry ground fault current and it probably will.