That is not your OP question.
A true mwbc 120v/240v circuit feeding gfci receptacles should meet the condition in post #9.In that case it can not function due to tripping of gfci.
That is not your OP question.
No,sir.I am afraid you missed something.Consider a mwbc 120v/240v circuit feeding two gfci receptacles,each gfci wired to the outer hot conductors,but, per the definition of mwbc,with the neutral on the load side of one gfci connected to the line side of other gfci.If the gfci receptacle with line side connected neutral supplies any load,it would trip the other gfci due to neutral current flow through it.
Respectfully,A true mwbc 120v/240v circuit feeding gfci receptacles should meet the condition in post #9.In that case it can not function due to tripping of gfci.
But al hildenbrand says (post#19)after gfci's,the circuit is no longer MWBC.It is a MWBC because that is what it was when it left the panel. What you do with the wires after they leave the panel will not change the character of the circuit. For example, when you get to the last outlet (i.e., furthest or most remote from the panel), all you will have is one hot conductor and one neutral (plus the EGC). You no longer have multiple hot conductors. If a person opened that outlet box and looked inside, they would only see these three wires, and think this was just a standard, single phase circuit. It is not, and the person would have to look further upstream to notice that multiple hot conductors shared a neutral when they left the panel, and continued to share the neutral up to the first junction box or outlet box they entered. Nothing that happens downstream from that point can change the fact that the circuit is a MWBC.
So?But al hildenbrand says (post#19)after gfci's,the circuit is no longer MWBC.
Respectfully,
This is wrong.
Again, the GFCI receptacle load side neutral cannot be spliced back to the LINE SIDE neutral. That GFCI, so connected, will trip the instant it is energized.
Respectfully, you must get two physical GFCIs and wire them. Even just one GFCI receptacle will, so connected, will demonstrate the error of your thinking.
While I am an electrical engineer, I am also a working, hands on the tools, electrician. What I am saying is physical GFCI receptacle beginners knowledge. One only has to hook up a physical GFCI like you describe once, and you will never do it deliberately again . . .
Then the whole circuit is not a mwbc.So?
That doesn't change the fact that a GFCI receptacle, or GFCI receptacleS, can be connected to an MWBC.
I am also saying the same thing and so a 120v/240v mwbc can not feed gfci receptacle because of tripping of gfci.
Very humbly and respectfully,I am also saying the same thing and so a 120v/240v mwbc can not feed gfci receptacle because of tripping of gfci.
No one is saying that it is.Then the whole circuit is not a mwbc.
Let?s go back to your post #9:A true mwbc 120v/240v circuit feeding gfci receptacles should meet the condition in post #9. In that case it cannot function due to tripping of gfci.
You are not describing the correct way to wire the receptacles, and that is why you are not understanding the situation. To be specific, the second receptacle is not, in fact, on the ?load side? of the first.Consider a mwbc 120v/240v circuit feeding two gfci receptacles, each gfci wired to the outer hot conductors, but, per the definition of mwbc,with the neutral on the load side of one gfci connected to the line side of other gfci. If the gfci receptacle with line side connected neutral supplies any load, it would trip the other gfci due to neutral current flow through it.
The circuit is a MWBC. Portions of it may only have one hot and one neutral, and those portions do not share the "multi-wire" characteristics of the circuit as a whole. But the circuit itself is multi-wire.Then the whole circuit is not a mwbc.
Haja, you are not seeing the circuit the same as the others, maybe this will help you understand what they are saying.
a) The MWBC feeds ONLY the line side of the GFI receptacles
b) On the load side of the GFI receptacle, the N. conductor can no longer be shared with the rest of the MWBC unless your protection is coming from multi-pole GFI breaker, not being provided by a GFI receptacle.
In my kitchen, I have three circuits serving receptacles on the countertop. They are separate circuits, and do not share neutrals. For each of the three circuits, I have two wires (one hot and one neutral) going from the panel to an outlet box. Inside that box is a GFCI receptacle, and the two wires are connected to its line side. From the “load side” of the GFCI receptacle, I have a hot wire and a neutral wire going to a second outlet box a couple feet away. These wires land on a standard (i.e., not GFCI) receptacle. When I plug something into the second receptacle, all of its current also flows through the GFCI receptacle upstream.To be specific, the second receptacle is not, in fact, on the “load side” of the first.
Is it possible that our friend Mr. Sahib is thinking of a MWBC being fed from 2 actual GFCI breakers as opposed to GFCI receps. He may not be aware that we typically use a GFCI recep and not a GFCI breaker as in the old days.