The bottom most diagram in that is exactly what I mean.You can easily see it is not mwbc:it has two separate neutral wires.
The NEC considerer's a circuit in how it is fed, not on how the circuit is used at the load end, in both those applications the circuit is a MWBC because it come from the panel from two different phases but share the same neutral, just because they split to two receptacle loads at the end does not change it from being a MWBC, even if you just only had the two GFCI's at the end since the sharing of the neutral on the line side of the GFCI's will not cause the GFCI's to trip, if you study the PDF file I posted you will see why, as you will also see why a two pole GFCI breaker will even allow a MWBC on the load side of the breaker, it done all the time, and has been for years.
Also after you have split into two separate circuits, it no longer meets the definition of a MWBC, but the NEC still treats it as one when applying the rules.
You agree that having two receptacles on a MWBC is still a MWBC, now replace those receptacles with two GFCI's and feed the MWBC to the line side only and you will still have a MWBC but with two GFCI's that will function, but after the GFCI's you can not share the neutral only on the line side, so to run load side receptacles from these GFCI's you must use a separate neutral for each circuit from each GFCI, as in the third diagram that I posted a link too.
Without knowing what was said in that book we can not clear up what your not understanding.
But if you study the PDF and pay attention to the 240 volt two pole description it should clear up what your not seeing, you first have to understand how a GFCI works, without that it will be hard to get you to understand what we are trying to tell you.