The listed breaker size is lower than the MCA.Where is the concern. Seems pretty straightforward other than the MCA seems high compared to rated currents
For one there is max fuse and max breaker which are very different. Why? The entire label is bizarre to me.
@augie47 I said the same thing at first...
From T430.52:I’ll have to look up the exact section in article 430, but max fuse size for motors is quite a bit larger than max breaker size, depending on the type of fuse.
I forgot about that table. But doesn't that mean the fuse should be less than the breaker-- assuming time delayI’ll have to look up the exact section in article 430, but max fuse size for motors is quite a bit larger than max breaker size, depending on the type of fuse.
From T430.52:
Non-time delay 300%, Time delay 175%, Circuit breaker 250%.