You could but as Little Bill said, the two circuits would have to be tied.I'm not sure I've seen this language. I believe you could have a 12/2-2 (4 insulated conductors) to a single box containing a duplex receptacle.
See 210.7
You could but as Little Bill said, the two circuits would have to be tied.I'm not sure I've seen this language. I believe you could have a 12/2-2 (4 insulated conductors) to a single box containing a duplex receptacle.
That is not required by NEC definition of a kitchen.Does it have an icebox?
2023 NECI'm planning a Mother-in-Law suite for a build. This MiL Suite will have a small kitchenette that includes a sink, microwave, and toaster. But no big appliances. I'm concerned that the AHJ may consider this a kitchen and require two small appliance branch circuits consistent with 210.11(C)(1). So I've been thinking of splitting the yoke on the countertop duplex receptacle and putting a separate branch on each receptacle.
I don't see anything in the code that slaps my wrist for this, but it feels iffy.
Thoughts?
Paul
I'm planning a Mother-in-Law suite for a build. This MiL Suite will have a small kitchenette that includes a sink, microwave, and toaster. But no big appliances. I'm concerned that the AHJ may consider this a kitchen and require two small appliance branch circuits consistent with 210.11(C)(1). So I've been thinking of splitting the yoke on the countertop duplex receptacle and putting a separate branch on each receptacle.
I don't see anything in the code that slaps my wrist for this, but it feels iffy.
Thoughts?
Paul
I'm thinking coffee maker at same time as one the other appliances you mentioned is even more likely to happen in something that is borderline whether it is an actual kitchen or not and is more of a personal space application like a MIL suite.I've previously suggested using a 2 gang box rather then splitting a single yoke for two circuit, even though code would permit splitting the single device for 2 circuits.
In a similar vein, I absolutely agree that this is not a kitchen by NEC definition. However I would absolutely run 2 circuits simply because it is really really nice to be able to run a 'toaster' (think countertop air fryer/toaster/oven) and microwave at the same time.
Jonathan
Yeah, if you got to pull in a circuit(s) then wire for future use but explain it to the home owner why you suggest it.I've previously suggested using a 2 gang box rather then splitting a single yoke for two circuit, even though code would permit splitting the single device for 2 circuits.
In a similar vein, I absolutely agree that this is not a kitchen by NEC definition. However I would absolutely run 2 circuits simply because it is really really nice to be able to run a 'toaster' (think countertop air fryer/toaster/oven) and microwave at the same time.
Jonathan