Does anyone see a problem with this box?
Fair enough.... Now... if you have no depth to play with, what do you do?peter d said:Assuming I just spent big bucks to get my basement finished, and that is the final result, then yeah, it looks horrible.
tallguy said:Fair enough.... Now... if you have no depth to play with, what do you do?
stickboy1375 said:![]()
infinity said:H 2.25
N 2.25
G 2.25
Device (2*2.25) = 4.5
Total 11.25
Yes, a device counts as two of the largest conductor attached to it.220/221 said:Thanks. I didn't realize that devices were double.
I was taught decades ago that the grounds combined were counted as 1 cu inch. Old wives tale or code change?
raider1 said:Typically you will be able to use the extra capacity of the luminaire canopy in conjuntion with the outlet box to provide adeaquate space for the conductors. (See 410.10)
Chris
stickboy1375 said:The way I read 410.10, is that it is for fixture wires only not branch circuit conductors... am I wrong to believe this? Probably why this box has no UL marking...
For those who aren't willing to pay for this... I rest my case. :roll:peter d said:In a concrete wall? Get out the hammer drill and start breaking!![]()
tallguy said:For those who aren't willing to pay for this... I rest my case. :roll:
raider1 said:Many luminaire canopies are marked with the voulme in cubic inches somewhere on the fixture. You are able to use the combine cubic inches of the canopy and the outlet box for you supply conductors and the fixture wires and mounting hardware.
Take a look at 314.16(A). This section states that the volume of a wiring enclosure shall be the total volume of the assembled sections and, where used, the space provided by plaster rings, domed covers, extention rings, and so forth, that are marked with their volume.
I would say that a fixture canopy that is marked with its volume would apply to this section.
Chris
lilg1964 said:I am building a room addition with concrete walls furred out with 3/4" foam insulation and have installed the B108B boxes due to the depth without breaking the concrete for the outlets. ...Has anyone used these boxes before?? I'd appreciate any help I can get.
jeremy stephens said:i need to get my transcrips from last year!