Dean83169 said:I was curious as to the method of figuring out how many cat 5 wires to fit inside a piece of EMT. Does the standard pipe fill follow the same rule or not since its under 24 volts. A few peeps said fill it to you cant fit anymore but I want the real answer please.
wbalsam1 said:A cable is treated as one conductor and can take up to 53% of the cross-sectional area of a raceway,
wbalsam1 said:I don't see a similar provision at Art 830.133(A)(1), though.
iwire said:It does not need an exception as Article 830.133 does not require the raceway to be installed per chapter 3 as 800.110 does.![]()
Article 725 and not 800 applies to computer cables. 725.3(A) makes the wire fill rules mandatory for CAT 5 cable.As far as the NEC is concerned as many as you can stuff in the pipe.
don_resqcapt19 said:Bob,
Article 725 and not 800 applies to computer cables. 725.3(A) makes the wire fill rules mandatory for CAT 5 cable.
Don
Dean83169 said:So which article applies to Cat5 cabling, 725 or 800? Because I see 800.110 exception can we all agree on this yet?
Most code authorties and the handbook say that CAT 5 is under Article 725.So which article applies to Cat5 cabling, 725 or 800?
DonThe installation requirements for the low-voltage wiring of information technology equipment (electronic data processing and computer equipment) located within the confines of a room that is constructed according to the requirements of NFPA 75, Standard for the Protection of Information Technology Equipment, are not covered by Article 725. Low-voltage wiring within these specially constructed rooms is covered in Article 645.
Also, if listed computer equipment is interconnected and all the interconnected equipment is in close proximity, the wiring is considered an integral part of the equipment and therefore not subject to the requirements of Article 725. If the wiring leaves the group of equipment to connect to other devices in the same room or elsewhere in the building, the wiring is considered ``wiring within buildings'' and is subject to the requirements of Article 725.
don_resqcapt19 said:Bob,
Article 725 and not 800 applies to computer cables. 725.3(A) makes the wire fill rules mandatory for CAT 5 cable.
Don
don_resqcapt19 said:Dean,
Most code authorties and the handbook say that CAT 5 is under Article 725.
From the handbook comentary...
Don
That being said CAT 5 is not an exact match to the scope of Article 725 either.800.1 Scope
This article covers telephone, telegraph (except radio), outside wiring for fire alarm and burglar alarm, and similar central station systems; and telephone systems not connected to a central station system but using similar types of equipment, methods of installation, and maintenance.
I guess I can say that CAT 5 is clearly not covered by Article 800, but is not clearly covered by Article 725. The basis for putting it under Article 725 is the word "singnaling" in the scope.725.1 Scope
This article covers remote-control, signaling, and power-limited circuits that are not an integral part of a device or appliance.
Dean83169 said:I was curious as to the method of figuring out how many cat 5 wires to fit inside a piece of EMT. Does the standard pipe fill follow the same rule or not since its under 24 volts. A few peeps said fill it to you cant fit anymore but I want the real answer please.