hbiss
EC, Westchester, New York NEC: 2014
- Location
- Hawthorne, New York NEC: 2014
- Occupation
- EC
Is BICSI even relevant anymore?
To some IT people it's like our NEC.
-Hal
Is BICSI even relevant anymore?
That one probably came from old systems, but today lives on because of mixed domain environments, and for unshielded cables cross talk is a big concern. Refer to the DCID 6/9 regulations.I've been trying to debunk that idea for years but I still keep hearing it. It probably came from IT people or BICSI who are "over the top" in their own world.
-Hal
Real 600V listed cable like Allen-Bradley 600 volt rated cat5 or 6 or whatever, might be considered by an AHJ/508A inspector as meeting Exception No. 1 , as the thick outdoor covering and the 600V conductors provide a 'permanent barrier':2017 NEC 800.133(A)(1)(c) said:Electric Light, Power, Class 1, Non–Power-Limited
Fire Alarm, and Medium-Power Network-Powered Broadband
Communications Circuits in Raceways, Compartments, and
Boxes. Communications conductors shall not be placed in any
raceway, compartment, outlet box, junction box, or similar fitting
with conductors of electric light, power, Class 1, non–power-
limited fire alarm, or medium-power network-powered broad-
band communications circuits.
Exception No. 1: Section 800.133(A)(1)(c) shall not apply if
all of the conductors of electric light, power, Class 1, non–
power-limited fire alarm, and medium-power network-powered
broadband communications circuits are separated from all of
the conductors of communications circuits by a permanent
barrier or listed divider.
So Rccranford1 in my experience even when people ignore or interpret the code, the signals just dont work well and its better to take another route.Is Cat 6 allowed in a JB and Conduit Run that also has 110 Volt Power? Please state code references.
Ummm, no. See 800.133(1)(d)
-Hal
What Code article covers RS-232 and RS-485 data communication wiring? Is it a class 2 circuit? Can serial data communication work on non twisted wiring like tray cable?Thanks for the code reference Hal, 800.133,
When I see 600V cat5 I tucked in with control panel stuff I am re-doing or servicing I look for a way to re-route and separate it completely.
I have techs argue with me that the 600V cat5 is a permanent barrier and meets the exception 1 in that section:
Real 600V listed cable like Allen-Bradley 600 volt rated cat5 or 6 or whatever, might be considered by an AHJ/508A inspector as meeting Exception No. 1 , as the thick outdoor covering and the 600V conductors provide a 'permanent barrier':
32 Feet cat5 CMX Rare 600 Volt rating. | eBay
Find many great new & used options and get the best deals for 32 Feet cat5 CMX Rare 600 Volt rating. at the best online prices at eBay! Free shipping for many products!www.ebay.com
Years ago I got into a debate with another 508 panel guy about reclassifying an RS232 as class1,he had it running over some 16 or 18 AWG TFFN so it could briefly pass thru a gutter that had some 120V circuits.
After that RS232 circuit proved to be unreliable I got to reroute it
So Rccranford1 in my experience even when people ignore or interpret the code, the signals just dont work well and its better to take another route.
What Code article covers RS-232 and RS-485 data communication wiring? Is it a class 2 circuit? Can serial data communication work on non twisted wiring like tray cable?
Thanks for the code reference Hal, 800.133,
When I see 600V cat5 I tucked in with control panel stuff I am re-doing or servicing I look for a way to re-route and separate it completely.
I have techs argue with me that the 600V cat5 is a permanent barrier and meets the exception 1 in that section:
Real 600V listed cable like Allen-Bradley 600 volt rated cat5 or 6 or whatever, might be considered by an AHJ/508A inspector as meeting Exception No. 1 , as the thick outdoor covering and the 600V conductors provide a 'permanent barrier':
32 Feet cat5 CMX Rare 600 Volt rating. | eBay
Find many great new & used options and get the best deals for 32 Feet cat5 CMX Rare 600 Volt rating. at the best online prices at eBay! Free shipping for many products!www.ebay.com
Years ago I got into a debate with another 508 panel guy about reclassifying an RS232 as class1,he had it running over some 16 or 18 AWG TFFN so it could briefly pass thru a gutter that had some 120V circuits.
After that RS232 circuit proved to be unreliable I got to reroute it
So Rccranford1 in my experience even when people ignore or interpret the code, the signals just dont work well and its better to take another route.
People have been putting that 600V ethernet in main panel's for a while now, I have argued against it and lost, AHJ accepts it based onMaybe give them 3 or 4 cycles. They're finally waking up and allowing ethernet in the main panel for power measurement. It's funny given the three worlds I live in it's a toss up who's slower to adopt any anygiven time. Engineering, Medicine, or the Military.
I was thinking of...People have been putting that 600V ethernet in main panel's for a while now, I have argued against it and lost, AHJ accepts it based on
800.133(A)(1)(c) Exception No. 1.
Read that exception, it does not require a listed chapter 3 wire type, all it needs to do is provide a permanent barrier that the AHJ accepts.
paulengr offers some good insights though.
There's no requirement or even practical consideration that requires separation or right angle crossing of ethernet twisted-pair wiring from normal power wiring.
Website - [I said:Written by Don Schultz, Technical Sales Representative and Fluke Networks Certified Technician[/I] ]
- When running unshielded data cable parallel to typical residential voltage power cables (120V or 240V AC for example), the NEC (National Electric Code) specifies it must be separated by at least 200mm or 8 inches.
No, that is for systems such as FiOS and only covers up to the interface unit (essentially the providers cables).
That does not seem to be the case because they call out 90.2 (B) so FIOS up to the ONT would be on the utility.No, that is for systems such as FiOS and only covers up to the interface unit (essentially the providers cables).
Guys, article 800 does NOT cover typical data/ethernet/cat5 wiring. That would be article 725.
645.3(D) Electrical Classification of Data Circuits.
Section 725.121(A)(4) shall apply to the electrical classification
of listed information technology equipment signaling circuits.
Sections 725.139(D)(1) and 800.133(A)(1) (c) shall apply to
the electrical classification of Class 2 and Class 3 circuits in the
same cable with communications circuits.
725.121(A)(4) Listed audio/video information technology (computer),
communications, and industrial equipment limited-power
circuits.
Informational Note: One way to determine applicable
requirements for listing of information technology
(computer) equipment is to refer to UL 60950-1-2011,
Standard for Safety of Information Technology Equipment.
Another way to determine applicable requirements for
listing of audio/video, information and communication
technology equipment is to refer to UL 62368-1-2014,
Safety of audio/video, information and communication technology
equipment. Typically such circuits are used to interconnect
data circuits for the purpose of exchanging
information data. One way to determine applicable
requirements for listing of industrial equipment is to refer
to UL 61010-2-201, Safety requirements for electrical equipment
for measurement, control, and laboratory use –Part 2-201:
Particular requirements for control equipment, and/or
UL 61800-5-1, Adjustable speed electrical power drive systems –
Part 5-1: Safety requirements –Electrical, thermal and energy.
725.121(C) Marking.
The power sources for limited power circuits in
725.121(A)(3) and limited power circuits for listed audio/
video information technology (equipment) and listed industrial
equipment in 725.121(A)(4) shall have a label indicating
the maximum voltage and current output for each connection
point. The effective date shall be January 1, 2018.