From the photos provided, to me it looks like rupture from the available fault current at the location. Are these panels near a large service?
Taking a look at the let through current chart
HERE and making an assumption that these controls are near a source of 20K available current.
Its not hard to see why some damage may be happening. The charts shows that for a 30A unit, the RMS let through fault current is 987A, with a 20,000A source. It's not hard to imagine a 30A CL CC fuse and block, having a hard time coping without some damage at those kinds of currents.
Once that fuse barrel ruptures and spews out a starting ball of plasma, the main 3Φ arc lights up across all phases. The fuses are closely spaced and are not enclosed. So their parts are fully available to the plasma ball, that is highly conductive, once it gets going.
In the first photo, every fuse and holder in the photo has some form of arc burn damage. Either on the fuse ferrules or the fuse clips. That's 5 fuses on each side of the one that ruptured. The the plasma ball was at least big enough to cover the width of 11 fuseblocks. At this point I would bet that the main feeding the controls would trip, hopefully. That's like a foot long ball of plasma, connected to the line side of 11 fuseblocks. The surrounding fuses contributed some of their load side current, until they also melted in the event.
In the second photo, even though it was the first in the row to rupture, the plasma ball still reached over 5 fuseholders to the right. The 5th one has burns on the upper clip. Looks pretty consistent in reach each time. Is that how many become engulfed before the main trips? I can't envision any good reason for it to go out, limiting itself to 5 holders, without the main putting it out.
Looks like you have #3/0 feeder cable, 200A, 277/480V and the loads are connected line to line, with no neutral used. That size cable can provide some serious arc power when connected close to a decent sized service.
Here is what I'm talking about, same cable size, same type conditions. Arc starting on the line side. Line to line fault, before the fuses.
You can see here that even the load side bus burned away. The enclosure sheet metal that is covering the actuation mechanism started to melt. What took this one out, was the pole transformers and primary fuses. 2 of the 3 pots had to be replaced. Plasma balls are some hot stuff, and don't go out easily, once they get started. The spacing between these lugs is about 1", much further than on those CC blocks. The plasma ball burned about the same 12" width of metal here, but much more ferociously.
Tell us more on how these lighting panels are supplied.
View attachment 19503
MTW