electricmanscott said:I would NOT pass this job if I was an inspector nor should any inspector with any competence.
With that logic you could build a house complete without wiring and then show up and say it's existing I don't have to do anything.
I hate to inform you of this but the inspectors here are very well qualified..
Here is what we are talking about..250.4 General Requirements for Grounding and Bonding. The following general requirements identify what grounding and bonding of electrical systems are required to accomplish. The prescriptive methods contained in Article 250 shall be followed to comply with the performance requirements of this section.
Section 250.4 provides the performance requirements for grounding and bonding of electrical systems and equipment. Performance-based requirements provide an overall objective without stating the specifics for accomplishing that objective.
now we read the requirements of the electrodes..
III. Grounding Electrode System and Grounding Electrode Conductor
250.50 Grounding Electrode System.
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.
now what I am saying is that when the foundation is already poured and I was not there and no one has an inspection sticker on the re-bar and no connection point is present..I am going to assume there is no legal re-bar present to connect to..just hammering away a piece of the foundation and finding some happen chance piece of re-bar does not constitute a legal re-bar installation..Unless you can verify the re-bar meets the requirements of this section you can not use it..So go ahead and not pass me I will call and have a senior state electrical inspector come out and pass the install and you will have to deal with the complaint process..It is not my responsibility to make sure the CG or HO install the re-bar correctly and have it inspected..how ever It is my responsibility to connect to all the metal that meets the code and can be verified at the time our company is hired..So if the re-bar does not meet requirements then I can not connect to it and unless it is inspected before the pour I have no way of knowing if it is legal or not..