- Location
- Massachusetts
For those that do not know CEE is short for Concrete Encased Electrode.
In my opinion it is a NEC violation to stub the rebar out of the foundation for connection to the GEC.
The facts as I see them.
250.52(A)(3) defines what a CEE is. That description requires that the CEE be surrounded by at least 2" of concrete.
Given that definition the rebar that is stubbed out is not a CEE. It is simply a steel conductor attached to the the CEE so in reality the stubbed out section is a GEC.
250.62 prohibits using steel as a GEC.
In my opinion and due to 250.64(A) the only legal way to connect to a rebar CEE is with a copper conductor connected to the rebar in the area defined by 250.52(A)(3).
All you 'stubbers' are in violation of the NEC. :grin: