I hope this will be my last post in this thread. I?ll try to sum up all my thoughts here. I have been trying to be completely objective and ascertain what the code literally says. Of course it may contain my personal bias and interpretation of the code. However, I have no motives or reason for leaning one way or the other. Rebar stub-ups are fine with me. This is purely a mental exercise to fathom, in my mind, exactly what the code says. You are welcome to believe anything you want. Thanks in advance to anyone who takes the time to read this.
First, 250.70 says that ?the grounding conductor or bonding conductor must be connected to the grounding electrode?? and then gives the methods in which it may be connected. The point is, a GEC or bonding conductor must be attached to the electrode.
Now, 250.52 contains descriptions of the various types of electrodes. These descriptions impact the permitted locations where a GEC or bonding conductor may be attached.
250.52(A)(1): This is the description of the waterpipe electrode.
1. A metal underground waterpipe
2. In direct contact with earth for at least 10 feet
3. Electrically continuous to the connection of the GEC/Bonding conductor
4. No grounding system connections can be made more than 5 feet from the point of entrance into the building.
So the actual electrode is the underground portion of the waterpipe. The GEC can be connected directly to the underground electrode. But the code also allows the GEC to be attached away from the electrode by stipulation #3 above, as long as it is within 5 feet of the entrance into the building, stipulation #4. This could certainly be above ground outside or inside the building.
There is a touch of confusion correlating 250.70 with the metal underground waterpipe. However, the waterpipe language above eases the restriction in 250.70 by stating that the GEC connection can be on any part of the waterpipe as long as it is electrically continuous and within 5 feet of the entrance to the building.
250.52(A)(2): This is a description of the building steel electrode.
1. The metal frame of the building that is connected to earth as detailed in this section.
So the entire steel frame is the electrode. Therefore, a GEC connection can be made to any point on the building steel. No issue with 250.70 here. Make the connection to the steel wherever is convenient.
250.52(A)(4): This is a description of a rod or pipe electrode.
1. Shall be at least 8 feet in length
2. If of pipe, shall not be less than 3/4"
3. If a rod, shall not be less than 5/8? diameter, if listed, can be 1/2?
So the entire pipe or rod if the electrode and the GEC connection can be made anywhere on the electrode. No issues with 250.70 here. The entire pipe or rod is the electrode, not just the buried portion. Sure, 250.53 talks about how much must be buried, but that does not change the fact that 250.52 says the entire pipe or rod is the electrode. So, connect to the rod or pipe wherever you want to.
Now we come to 250.52(A)(3). 250.70 says the connection must be made to the electrode. So what is a rebar electrode by 250.52(A)(3)?
Well, the code says it is rebar encased in concrete. Period. (We?ve already gone over the 6 requirements. No need for that here. The relevant thing is that the rebar must be encased.) 250.70 says the GEC must be connected to the electrode, therefore the GEC connection must be made in the concrete.
A rebar stub-up does not meet the requirements for a CEE. So the GEC cannot be attached to the stub. It must be attached to the concrete-encased electrode. This section gives no provisions for a GEC connection away from the electrode as the waterpipe language does. This section says that the electrode must be encased in concrete. And 250.70 says the GEC must be connected to the electrode. And this can only happen by a connection in the concrete.