You can't install any wires in the rod according to your reference.
Maybe WE cant, but the fan manufacturer can.
JAP>
You can't install any wires in the rod according to your reference.
Maybe WE cant, but the fan manufacturer can.
JAP>
You can't install any wires in the rod according to your reference.
Sure I can, it's part of asembling the fan. That's not anything at all like running conduit and conductors to the fan box on the ceiling.
And you are doing the same thing when you rewire the fan.But you're not 'just' assembling the fan. You're altering it.
But you're not 'just' assembling the fan. You're altering it.
If the rod is to "expressly" run the wires, then what holds the fan up?
And you are doing the same thing when you rewire the fan.
You'd rather rewire the fan I'd rather splice the wires, we're both going to hell for altering a listed item.
Splicing in a raceway is an issue especially when the raceway is long and you need to pull wires out however, slicing in a short run fan outlet may or may not be a violation- it probably is since it is a listed unit. I have made the splice and I see no possible danger from doing this.
Welcome to the Forum, Bill.I am a new member to this forum and this is my first question.
In certain cases the height of a ceiling requires the fan to use a longer downrod than was originally supplied with the fan. . . . I guess my basic question is, is the downrod considered a raceway?
"A complete lighting unit consisting of a light source such as a lamp or lamps together with the parts designed to position the light source and connect it to the power supply. It may also include parts to protect the light source or the ballast or to distribute the light. A lampholder itself is not a luminaire."
410.56 Protection of Conductors and Insulation
410.56(C) Luminaire Stems. Splices and taps shall not be located within luminaire arms or stems.
410.64 Luminaires as Raceways. Luminaires shall not be used as raceways unless they comply with 410.64(A), 410.64(B) or 410.64(C).
With all due respect, I doubt seriously the code rule for not being able to splice within a raceway has anything to do with a need for mechanical strength if one were to want to pull the wire out.
JAP>
410.56 Protection of Conductors and Insulation
410.56(C) Luminaire Stems. Splices and taps shall not be located within luminaire arms or stems.
410.64 Luminaires as Raceways. Luminaires shall not be used as raceways unless they comply with 410.64(A), 410.64(B) or 410.64(C).
Well, it has to do with the failure due to the splice being installed under tension. Also a double splice- which I have seen leaves wire inside the conduit that cannot be removed. We had to use a backhoe to pull the wires out at a stone crushing plant. Fortunately, there was only one set of splices--
I have never seen that with the hundreds of fans I have installed; they pass through the center of the motor and terminate in the switch compartment where the light kit mounts.Usually the fans have a section where the downrod is connected that is large enough an area to make the splices...
is the down rod part of the fixture and are you extending the fixture wiring or are you bringing the branch circuit wiring down to the fixture?