Cellular Communication Utilities

Chadwick

New member
Location
nj
I am a Cellular Phone Tower Electrical Contractor for T-Mobile, Sprint, AT&T, Verizon, Ect. I have a few Questions: I am currently reading ?Limited Energy & Communications Systems? 2014.


1- Are the Cell Phone Carriers considered a ?Communication Utilities?? 90.2.B.4 (page 4)
2- If they are, would that make all of their equipment exempt from the NEC? (p10 question 6)

3- If they are Exempt from the NEC, then dos the AHJ not have the authority to approve or reject the installations or equipment that were designed by the cellular carrier from the Antennas, cabling from the antenna to the Equipment Cabinet, and the Equipment Cabinets, along with the equipment in the cabinet?
 

Attachments

Last edited by a moderator:

charlie b

Moderator
Staff member
Location
Seattle, WA
I approved the post, but I first removed the link to the company web site. We don't allow any form of advertising, and such links constitute advertisements.
 

kwired

Electron manager
Location
NE Nebraska
I would like to think that the service, feeders, standby generator, and other general power equipment is not exempt from NEC.

Actual communication equipment beyond incoming power supply termination - maybe is exempted.

This would somewhat equate to utility owned power generation facilities, wiring of the general lighting, air conditioning, other common aspects are typically covered by NEC, but the power generation equipment itself is exempted.
 

ceb58

Senior Member
Location
Raeford, NC
I would like to think that the service, feeders, standby generator, and other general power equipment is not exempt from NEC.

Actual communication equipment beyond incoming power supply termination - maybe is exempted.

This would somewhat equate to utility owned power generation facilities, wiring of the general lighting, air conditioning, other common aspects are typically covered by NEC, but the power generation equipment itself is exempted.
That is exactly how it is with our communication sites. The buildings are pre fab and wired in the factory with the panels, UPS and all branch circuits. It is then inspected by a 3ed party inspector and has their inspection label on the main panel, just like a mobile home. When the building is set the meter/service disco and the generator are field installed and inspected by one of our State inspectors. As far as the actual communication equipment the inspector has no jurisdiction over it because it is listed and approved equipment.
 

ActionDave

Moderator
Staff member
Location
Durango, CO, 10 h 20 min without traffic from wing
Occupation
wire pulling grunt
I would like to think that the service, feeders, standby generator, and other general power equipment is not exempt from NEC.

Actual communication equipment beyond incoming power supply termination - maybe is exempted.

This would somewhat equate to utility owned power generation facilities, wiring of the general lighting, air conditioning, other common aspects are typically covered by NEC, but the power generation equipment itself is exempted.
That is exactly how it is with our communication sites. The buildings are pre fab and wired in the factory with the panels, UPS and all branch circuits. It is then inspected by a 3ed party inspector and has their inspection label on the main panel, just like a mobile home. When the building is set the meter/service disco and the generator are field installed and inspected by one of our State inspectors. As far as the actual communication equipment the inspector has no jurisdiction over it because it is listed and approved equipment.
I agree. To throw a little wrinkle in things, the pics look like an open site so there is no building to house everything. I have only worked on one site like this, however, I think the same principal applies... once you get past the service the NEC stops.
 