I have used the results of this survey as part of the argument for labeling receptacles in other than Data Processing areas that are fed with UPSs. The survey indicated that about 24% of experienced electricians would not expect receptacles in a house with the main power off to be energized.
ADDED TEXT
100 I Fixed Wiring. Conductors, raceways, etc. installed under Chapter 3 methods.
110.27 Uninterrupted Power Supply (UPS) Connected to Fixed Wiring.
(A) Labeling.
(1) When a UPS supplies fixed wiring, each place the UPS supplied circuit(s) is accessible shall have a clearly legible marking in letters not less than 6 mm (? in.) high reading ?UPS Supplied?. The label shall comply with 110.21(B).
(2) When a control panel contains a UPS which supplies current to fixed wiring external to the control panel, the control panel shall have a clearly legible sign in letters not less than 6 mm (? in.) high reading ?Caution this panel contains a UPS?. The sign shall comply with 110.21(B).
(B) Disconnecting Means. A disconnect meeting the requirements of 110.25 shall be installed for all output circuits from the UPS.
Exception: The requirements 110.27 do not apply to areas meeting all the requirements of 645 Information Technology Equipment or 646 Modular Data Centers.
SUBSTANTIATION
90.1(A) Practical Safeguarding. The purpose of this Code is the practical safeguarding of persons and property from hazards arising from the use of electricity.
The recent introduction of fixed wiring in buildings fed from UPSs in other than Information Technology Equipment areas has introduced a new hazard. Until recently when you opened the main service disconnect for a building you would be able to assume that fixed wiring was no longer energized. APC and other manufacturers are selling UPS accessories for their products to facilitate connection to fixed wiring. (For example see
http://www.apcmedia.com/salestools/A...8L95_R0_EN.pdf). This installation guide does not require an output disconnect.
The recent introduction of UPSs embedded in control panels which feed external fixed wiring presents a similar hazard. I have directly experienced a case of this sort. I was tasked to replace a shunt-trip 3-pole circuit breaker with trip alarm contacts. I opened all the circuits serving the control cabinet. I measured the voltages on the circuit breaker power connections, the shunt-trip, and the trip alarm contacts. I found that the shunt-trip circuit was de-energized, but that the trip alarm contact was still energized. I opened the control cabinet (not something I normally would do, because the cabinet and associated equipment were maintained under contract by a third-party). I found that a standalone style UPS like one might buy in a big box store was inside and its output was energizing the trip alarm contacts. I also confirmed that all external power to the control panel was indeed turned off.
I am proposing the addition of
110.27 and the associated
100 I Fixed Wiring additions to the NEC to warn electricians of these new hazards. I am suggesting the use of ?UPS supplied? as labeling for receptacle outlet covers (and other covers) because it also serves as useful label for non-electrician users.
The exception is proposed because those qualified personnel working in 645/646 areas are already expecting UPS supplied receptacles.
Basis for 100 Fixed Wiring
Terms akin to Fixed Wiring are used in:
220.14(H) Fixed Multioutlet Assemblies.
250.34(C)(3)<info note> Fixed wiring systems
393.6(B)(4) fixed wiring methods
400.8(1) fixed wiring method
411.3(B)(5) fixed wiring method
500.8(B)<info note> fixed wiring
501.140(A)(2) fixed wiring methods
505.17(A) fixed wiring methods
511.7(A)(1) fixed wiring
511.16(B)(2) fixed wiring system
513.7(A) fixed wiring
513.10(C)(1) fixed wiring
513.10(D)(1) fixed wiring
513.16(B)(2) fixed wiring system
515.7(A) fixed wiring
516.7(A) fixed wiring
517.61(A)(3) fixed wiring
518.4(A) fixed wiring methods
518.4(A)<except> fixed wiring methods
520.5(A) fixed wiring method
520.5(A)<except> fixed wiring methods
530.31 fixed wiring
550.19(A) fixed-type wiring methods
550.32(D) fixed wiring method
620.21(A)(2)(b) fixed wiring
Basis for UPS labeling
I posted a poll on
forums.mikeholt.com/showthread.php?t=148012 which asked in essence ?would you check for voltage at receptacles and switches after turning off and locking the service main??. There were 26 responses to the poll, 5 said they would NOT check, basically 24%. Three who chose a testing method said they would not turn off main for various reasons. The poll was posted in the Safety forum to bias the answers towards testing.
Changing switches and receptacles
Let's assume you've got a job that consists of changing the receptacles, switches, and cover plates throughout a house from ivory to almond. You ask why and the guy who hired you said it is a directive from "She Who Must Be Obeyed". They are going away for the week. So you show up and decide the simplest way to do this is to put on a head lamp and turn off the main breaker. You turn it off and padlock it.
View Poll Results: Now when you go to each box, what do you do?
Voters 21. This poll is closed
test for voltage with a non-contact voltage stick 6 28.57%
test using a wiggly 5 23.81%
test using a Digital Volt Meter 5 23.81%
test using a shorting plug (for receptacles) 0 0%
test? are you crazy, the power is off! 5 23.81%
The response from CMP-1 limited itself to the original example (an elevator control panel, and not to the general cases supplied above).
Panel Statement: The problem identified by the submitter relates to product
design and marking rather than installation. In addition, the submitter is
proposing specific requirements in the general section of the code which may
be more appropriate in other sections of the code. In sections such as
620.52(B), the submitter?s concerns are addressed.