Hey I just want some feedback on these calcs. for services
388a load and 365a load.
I'm thinking 400a services including 400a main breakers. USE/RHW dual rated, paralleled, 4/0 copper conductors with 460a total ampacity - adjusted for ambient temps of up to 104 degrees = 404.8 ampacity