How about some NEC references for any of that??
My only reference is this article:
https://www.apc.com/salestools/KSIH-6Y6UU5/KSIH-6Y6UU5_R0_EN.pdf
How about some NEC references for any of that??
My only reference is this article:
https://www.apc.com/salestools/KSIH-6Y6UU5/KSIH-6Y6UU5_R0_EN.pdf
Please try to stay on topic. The OP was about the NEC load calculation, so it doesn't matter what you think is overkill or what might/should be or if the compressor has polka dots on it.
I do not believe the article in my last post is against the intent of NEC or is not on topic.
Please clarify, if possible.The article isn't relevant to Chillers.
That is AHJ's call.Nor does it completely follow the NEC.
Please clarify, if possible.
That is AHJ's call.
The original question was about Chillers. The article you linked is about Air Conditioners.
No it's not. The NEC tells you how to calculate MCA and MOCP. The article you linked doesn't follow the NEC requirements.
Thanks for your response. I wonder whether i)NEC distinguishes between air conditioner and chiller
and ii)UL or third party certifying authority would pass a product design also based on this article
No (except for the special provisions for room air-conditioners.) It distinguishes between motor operated equipment with a heretic refrigerant motor-compressor and equipment without.
Nobody would pass a product design based on this article. It's just an article, and not a very good one.
Sorry, it is not clear how the article is not applicable to ''chillers''.
UL or other third party certifying agency would test such a product design anyway for any danger to life and property. There would be none.......
It distinguishes between motor operated equipment with a heretic refrigerant motor-compressor and equipment without.
It doesn't mention "chillers" anywhere in the article. Where would you find a chilled water chiller?
The calculations in the article are based on UL standard. ( Post#31).They would test a product to UL standards, not to what this article says.
Mostly yes, if there is hermetic compressors involved art 440 usually applies.NEC requirements for air conditioners (other than room air conditioners) and chillers are same. So the article about air conditioners is also about chillers.
Ok I was finally able to track down the datasheets for these chillers. Chiller rated capacity is 348 (assuming tons) with 205kW at rated 100% load.
The datasheet gives the following: Compressor RLA = 124/158A, MCA=321A, MOP=450A. (3) identical chillers with these values.
I'm not quite sure what the RLA would be provided with (2) different values? These would lead to two very different feeder calcs.
New Feeder Calc using 124A RLA will be: 321A + 124A + 124A = 569A
New Feeder Calc using 158A RLA will be: 321A + 158A + 158A = 637A
Am I looking at these feeder calcs right based off of this new information? Which RLA value to use will have a pretty significant impact in that it will determine weather we are over/under the 600A threshold which will have impact on breaker rating, ATS rating, etc......
Thanks for the help!