Then what is the issue with the ferrous locknut in posts 8, 9, 11, 12?
cf
cf
Then what is the issue with the ferrous locknut in posts 8, 9, 11, 12?
cf
Here is some data pulled from Soares Book of Grounding, showing the approximate impedance of several sizes of GECs through conduit, both unbonded, and bonded at each end.
The impedance pretty much doubles if run through an unbonded ferrous conduit.
Rob,Maybe be it's just me but after looking at that chart it seems like a few metal straps would have no significant impact on the impedance.
Rob,
I don't think that chart is really talking about the AC impedance. It looks like they are just looking at the reduction in resistance that occurs when you parallel the raceway with the conductor.
Rob,
I don't think that chart is really talking about the AC impedance. It looks like they are just looking at the reduction in resistance that occurs when you parallel the raceway with the conductor.