I really like this solution. Not sure about space in the room, but can certainly check. ThanksIf the panel is located too high, you can raise the floor by providing a permanent sturdy platform to stand on. If it is at least 30x36 it covers the required working space. The highest breaker in the panel was 91" which is 12 inches too high. A 12" tall platform is needed. I would suggest guard rails at that height. The platform could be made of concrete, wood, metal, or any other building material.