Scott,
What am I missing when I read the NETA spec you quoted and the information in the SquareD document that I linked to in an earlier post says?
It seems to me that UL is saying a rise of up to 50 ?C at the termination points is permitted by the standard.
Few things here, 1st the Ul is a max spec, part of the design basis, the delta T's I posted are for IR scanning and recommended actions (Apples and Oranges).
IR scanning wont give you the real temp, just surface temp, the actual conductor core temp will be higher.