OK, here is the set up...
Siemans Sentron (?) 225A 3PH 480V circuit breaker in a MDP feeding a lighting panel.
Lighting panel also has a second 225A 3PH 480V Sentron Circuit breaker.
This installation has not changed in 3 years. No new load has been added to that panel. Panel is feeding all HID lighting.
About a week ago the 225A breaker in the MDP tripped...It reset, took quick readings on the feeders...A- 183A, B-154A, C-138A...Planned to come back and balance the load a little better.
We haven't gotten back yet...Today it tripped 2x in a span of 45 mins....I got on site and the breaker had reset and was on. I got the same readings on the phases.
Visually checked the connections on both breakers, nothing looked odd...no burning, etc.
Checked the individual cb's...found 5 breakers that had 17-17.5 amps load, and one that had 21.5 amps load. These are all 20A 1P, and all on phase A...
I was able to shut off the circuit with 21.5A and get the loads down to 158ish, 155ish, 140ish....
Now here is the questions...
1) why would the breaker in the MDP trip? instead of the main in the panel? I wasn't able to really open anything (it's a large retail store and they were open) to see if there is an adjustable trip setting on the sentrons...
2) is it possible that the overloaded 1P's have any effect on it?
3) short of just replacing $700 circuit breakers, what should I look for?
thanks
edit to add - it appears that each leg has an adjustable trip setting
Siemans Sentron (?) 225A 3PH 480V circuit breaker in a MDP feeding a lighting panel.
Lighting panel also has a second 225A 3PH 480V Sentron Circuit breaker.
This installation has not changed in 3 years. No new load has been added to that panel. Panel is feeding all HID lighting.
About a week ago the 225A breaker in the MDP tripped...It reset, took quick readings on the feeders...A- 183A, B-154A, C-138A...Planned to come back and balance the load a little better.
We haven't gotten back yet...Today it tripped 2x in a span of 45 mins....I got on site and the breaker had reset and was on. I got the same readings on the phases.
Visually checked the connections on both breakers, nothing looked odd...no burning, etc.
Checked the individual cb's...found 5 breakers that had 17-17.5 amps load, and one that had 21.5 amps load. These are all 20A 1P, and all on phase A...
I was able to shut off the circuit with 21.5A and get the loads down to 158ish, 155ish, 140ish....
Now here is the questions...
1) why would the breaker in the MDP trip? instead of the main in the panel? I wasn't able to really open anything (it's a large retail store and they were open) to see if there is an adjustable trip setting on the sentrons...
2) is it possible that the overloaded 1P's have any effect on it?
3) short of just replacing $700 circuit breakers, what should I look for?
thanks
edit to add - it appears that each leg has an adjustable trip setting
Last edited: