iwire said:So you watched the meter for 3 hours straight on each of those loads.![]()
yeah...i'm still watching..
unless MH fixtures draw less after they are on for awhile, i'll stick with my original story
iwire said:So you watched the meter for 3 hours straight on each of those loads.![]()
emahler said:i don't believe there was a fault...i believe that there was an overload condition...remember phase A was reading 184A...the rated continuous load for these breakers are 180A...
i just found it interesting that there were multiple branch circuits with continuous loads of over 16A....one of them with a continuous load of 21.5A...on a 20A CB....
Only believe what you can measure and document. Starting with an assumption, while often helpful, can sometimes lead you down the garden path. Since this is happening so frequently now, put a recorder on it and settle the matter once and for all.emahler said:i don't believe there was a fault...i believe that there was an overload condition...
76nemo said:Fault meaning semi-instant OL, that's why I asked about new additional loads on circuit.
mdshunk said:Only believe what you can measure and document. Starting with an assumption, while often helpful, can sometimes lead you down the garden path. Since this is happening so frequently now, put a recorder on it and settle the matter once and for all.
breaker might be getting weaker due to the load being over 80% for years. we just recently had a 20 amp 277 volt breaker in a lighting panel trip that had a load of 19.8 amps and it was fine for a few years then recently it started to trip over and overemahler said:newest added load was about 3 yrs ago...
emahler said:yeah...i'm still watching..
unless MH fixtures draw less after they are on for awhile, i'll stick with my original story![]()
celtic said:When is the last time they were relamped, ballast...etc?
3 yrs ago?
celtic said:Does the lighting ckt/s cause the MDP to dump?
macmikeman said:Went back and re-read the first post and found my question there, so this reply is a 10 characture dump. Sorry gang.
quogueelectric said:Is there a ground fault relay on the main and what is the voltage on the smaller 20 amp breakers??? Does the main have an adjustable trip?? they are usually shipped in the lowest setting>..
celtic said:You had mentioned some CBs in #1 and then some MH fixtures in #21.
I'm wondering if the CB's were for those MHs(and the relamping/reballasting timeframe).
We had an interesting situation a few years back with some site lighting....you name it went wrong....from wrong taps to GF situations to fixtures exploding....the MDP 1/4 mile away was tripping ~ through multiple OCPDs that did NOT trip.
macmikeman said:Hello Erik , and by the way, would it be possible to rig up a fused disco at the front end for a temporary bypass to see if there really is a problem other than mr. main breaker? (Dear code guru's, this is just a random thought, I have not given it much consideration to see if such an adventure would violate one of the many hundreds of codes it probably would). Most shops like how mine used to be have at least a doz. fused s/s cans and a bunch of fuses laying around the back room someplace. Fuses can blow faster than breakers given the right choice, and therefore a safe test done on the main feeders.