Re: Circuit Breaker wires

Only one unless the circuit breaker is listed for more than one. I'm pretty sure it has to be marked on the circuit breaker if the terminal will accept more than one conductor.

I'm looking for the code but I havn't found it yet.
 
Re: Circuit Breaker wires

It depends on the size and manufacturer. Some Sq D and C-H breakers in the 10 through 30 amp range are listed and identified for up to two conductors #14 through #10, Large frame breakers can accept up to four (or more) parallels in the KCMIL ranges.

Roger
 
Re: Circuit Breaker wires

Sam, look in 110.14(A).

BTW, you snuck that post in on me. ;)

Roger
 
Re: Circuit Breaker wires

You know I had an application which the electrician supplied a circuit with two different breakers, and I got a nice little shock. I know that't not the same thing, but other than not being able to connect it to an adjacent load on the same circuit, what's the purpose of this?

I got over the shock, by the way. :)
 
Re: Circuit Breaker wires

I've never heard of it. I would think it's not allowed but I'm not sure. :confused:
 
Re: Circuit Breaker wires

Originally posted by lady sparks lover:
You know I had an application which the electrician supplied a circuit with two different breakers, and I got a nice little shock. I know that't not the same thing, but other than not being able to connect it to an adjacent load on the same circuit, what's the purpose of this?

I got over the shock, by the way. :)
Patricia, I'm glad you didn't get hurt bad.

What you describe is a true violation of 240.8, and although it could have it's merit in current dividing and increasing the load on a circuit to double with out overloading the conductor, (assuming all is equal to the center of the circuit) the dangers outweigh the benefits. Think double fed ring circuit.

Roger
 
Re: Circuit Breaker wires

Sounds like someone double fed a circuit and they were on the same phase unknowingly or they knew it and swapped phases on one of the breakers so they didn`t have to find the double feed :eek: Sad but true some guys will fix that problem this way and to me it is a life threatining way :eek:
 
Re: Circuit Breaker wires

I had a service call once where I discovered a dual-fed circuit. I disconnected and capped one of the wires at the panel.
 
Re: Circuit Breaker wires

short of tearing the entire place to pieces there is one other thing you could have done and that is to joint them in a panel and make one termination.Does that make them parralleled I don`t think so unless they end up at same place ;)
 
Re: Circuit Breaker wires

Originally posted by allenwayne:
short of tearing the entire place to pieces there is one other thing you could have done and that is to joint them in a panel and make one termination.Does that make them parralleled I don`t think so unless they end up at same place ;)
Allen, why not do what Larry said or simply put both wires on one breaker (if it's identified for two) and save the wire nut?

Roger
 
Re: Circuit Breaker wires

If the breaker is listed for 2 sure but as far as I know only 2 brands are.If one I just didn`t add that part sorry :eek: I should know better with this crew of forumaholics :D
 