weressl
Esteemed Member
"Creo que no, Timoteo":roll:
There is little in the code requiring 'technically sound". In fact one might think 90.1.B (2008) suggests one may be about as moron as one wishes - just so long as the installation is essentally free from hazards
Assuming this comment applies to using adequately protected single conductor type W: How is this "TECHNICAL(L)Y wrong and and potentially DANGEROUS"?
JFTR I would go with your recomendation, 3C - w/G, type G, 4/0. It is fairly common and not too bad to handle - as long as it was direct connected and the installation did not require a cord and plug connection.
ice
Three/Four conductor cables assure that the cable lengths for each phase conductor are close to equal, and routed along the same physical path: the rule for parallel cables. If you understand the function of the two requirements there, the same applies here.