mstrlucky74
Senior Member
- Location
- NJ
Have a situation where a floorbox has (3) receptacles and (2) are fed from one panel and the other is fed from another panel. Is it code to put these conductors in the same raceway? Thanks.
As long as one is not an emergency circuit, yes.
Too many variables ......
You should not need but one "standard" grounding means for the assembly, and that could be any 250.118 method including a raceway.
If a separate IG is needed for each IG receptacle is a design issue not necessarily a Code issue.
For derating you only count the current carrying conductors. For pipe fill you count every conductor in the pipe.Yes it's a design thingy......so according to the design are those counts correct? Thanks