Circuits from different panels in same raceway

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Have a situation where a floorbox has (3) receptacles and (2) are fed from one panel and the other is fed from another panel. Is it code to put these conductors in the same raceway? Thanks.
 
So let me ask this....if you had a floorbox with (2) IG receptacles and (1) regular receptacle how many wire would this be? Would each IG have to get 1H+1N+1G+1IG? So that would be (8) wires for the IG's? Thanks.
 
Too many variables ......
You should not need but one "standard" grounding means for the assembly, and that could be any 250.118 method including a raceway.
If a separate IG is needed for each IG receptacle is a design issue not necessarily a Code issue.
 
Too many variables ......
You should not need but one "standard" grounding means for the assembly, and that could be any 250.118 method including a raceway.
If a separate IG is needed for each IG receptacle is a design issue not necessarily a Code issue.

Yes it's a design thingy......so according to the design are those counts correct? Thanks
 
Also keep in mind that you can't hare any neutrals between circuits that are fed from different panels and neutrals have to connect in the same panel where the circuit originates.
 
Status
Not open for further replies.
Top