D davidmicaiahca New member Jul 19, 2003 #1 If the insulation of a class 2 wire is rated at 600 volts, can it be in the same conduit as a class 1 wire?
If the insulation of a class 2 wire is rated at 600 volts, can it be in the same conduit as a class 1 wire?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jul 19, 2003 #2 Re: class 1 and class 2 wires See 725.55 Don
P pierre Senior Member Location Westchester County, New York Jul 20, 2003 #3 Re: class 1 and class 2 wires David Some people will refer to 330.3(C)(1) and think that the insulation rating is the key. As Don has posted, 725.55 is where you will find your answer. Read to understand, not for speed. Pierre