There is no necessity for a flexible connection for that type of equipment.(2) Flexible Connections.
Where necessary to employ flexible connections, as at motor terminals, one of the following shall be permitted: ...
The light fixture is mounted on an adjustable bracket so I hoping that would be seen as a necessity for that flexible connection.Just having splices does not trigger a requirement that the enclosure have seals. However, I highly doubt that I would approve the cord connection for that fixture as I do not see the installation being permitted in 501.10(A)(2).
There is no necessity for a flexible connection for that type of equipment.
And because of the low ceiling we could not mount them on the ceilingThe light fixture is mounted on an adjustable bracket so I hoping that would be seen as a necessity for that flexible connection.
View attachment 2564420
This picture show how the light was originally mounted but the light would have been shining right in your face so I elected to use an adjustable mount with the flexible connection.
Will do.. Thanks for the help!I would have to see the actual installation, but might require a flexible coupling in place of the flexible cord. But also might accept the cord. You need to run this by your AHJ.